Default Existing 200 amp Main Panel Adding 100 amp Sub Panel

I am wanting to install a new 100 amp subpanel to an existing 200amp main panel. I went to Home Depot and recently purchased a 100 amp panel that has a 100 main breaker already installed in that box. Is that ok to use as a subpanel? Also what gauge wire should I use to run to the sub? Do I ground the new sub or run the ground back to the main panel?

I appreciate any help you can give me.
Reply With Quote
  #2   IP: 65.73.69.95
Old January 28th, 2006, 04:04 AM
6pack 6pack is offline
Senior Member 'Self Help Master with Distinction'
 
Join Date: Oct 2002
Posts: 1,781
Default

Where do you intend to install the SUB?
What additinal wiring are you installing? Reason for SUB?
Different rules aply for the above and you may need a load calculation.
Reply
Reply With Quote
  #3   IP: 70.130.135.251
Old January 28th, 2006, 06:33 AM
Longo Longo is offline
Junior Member
 
Join Date: Jan 2006
Posts: 2
Send a message via Yahoo to Longo
Default reply

Sub is being added because of new addition. New sub is going to be located directly behind the 200 amp service. New wire going through previous concrete foundation wall and new sub mounting to new studed wall for new addition. Basically back to back just two walls between them. Outside service was buried to house and upgraded to 400 service. New power reguirements is just going to be used to power can lights, recepts, water heater. nothing real crazy. 27 x 37 addition, two floors, two baths, two bedrooms and large family room.
Reply With Quote
  #4   IP: 24.16.225.236
Old January 28th, 2006, 10:17 AM
suemarkp suemarkp is offline
Super Moderator

 
Join Date: Dec 2003
Location: Kent, WA
Posts: 8,264
Default

Since this sub panel is feeding a different part of the same structure as the service, you have to run a 4 wire feeder. You didn't have to buy a main breaker panel, but there is nothing wrong with using it (it just cost you more).

The next question is how many amps do you really need in that box. You can't have more than 100, but you are allowed to have less if you need less. Least inexpensive feeder will probably be 60A using #6 copper wire. If you want the full 100A, the size gets confusing. You can use #3 copper if individual wires if they have at least one H in the type, #2 copper if romex, and #4 SER or individual THHN wires if table 310.15(B)(6) is allowed in your area for this application. Since the subpanel will be close to the main, I'd try to run a 1.25" conduit if possible (PVC or flex metal) and use individual THHN wires.

The 4th grounding wire doesn't have to be as large as the other wires. For a 60A feeder, it only has to be #10 copper. For 61A to 100A, it must be at least #8 copper. No ground rods will be needed for this panel. You will most likely need to buy an accessory grounding bar though, because with the 4 wire feed the neutral and grounding wire must be on separate busses. Also, do not install the green bonding screw into the neutral bus, as that must be electrically isolated form the chassis in this application. On your individual circuits, put the white and bare wires on their respective busses -- they can't share a common bus like in a main panel.
__________________
Mark
Kent, WA
Reply With Quote
Reply






Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -4. The time now is 11:50 AM.


Powered by vBulletin® Version 3.6.7
Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.
© 2002 - QuinStreet, Inc.
http://www.selfhelpforums.com