Default Lights Dimming when AC comes on

I have had the HVAC guys out here for three days to work on my AC system because the lights dim when the AC comes on. So far, what they have done is replaced the piston(I assume in the compresson), chased what they thought was a kinked line(busted up my brick for this) and complained that the pressures were to low and to high on the high and low sides. All that and all they have accomplished is to get the shorten the length the lights dim(it's more like a flash now).

There current thought is that the panel in the garage needs to be re-wired. They said it might be that because the 60 amp breakers are on the top, they are pulling too many amps and the ones below it are the lights dimming. So they think the breakers need to be moved to the bottom. Having a electical/electronic degree, I know this is not going to help. They have that question out to a electrician themselves.

We had this house built and have been in it for a month. Are there other things I can have them check on? Can this really be an electrical problem.

Thanks in advance!
Reply With Quote
  #2   IP: 65.112.80.200
Old October 3rd, 2003, 01:05 PM
imported_trinitro imported_trinitro is offline
Senior Member
 
Join Date: Dec 2002
Location: Illinois
Posts: 106
Default

Unless you have a very large service (400A) and a dedicated transformer some dimming is unnavoidable. It's not bad, just annoying. The larger the AC the bigger/longer the dimming. Changing the location of the breaker won't make any difference. Since this is a new house it probably has at least 200A service, so perhaps the utility's transformer has too much load (i.e. too many houses).
Reply With Quote
  #3   IP: 148.78.243.122
Old October 4th, 2003, 08:55 AM
Wgoodrich's Avatar
Wgoodrich Wgoodrich is offline
Super Moderator

 
Join Date: Sep 2002
Posts: 7,451
Default

I did not see if this was a new home or older home. However answer wouild be the same.

If it were me I would go to the following link and perform a demand load calculation to find the minimum service size you are required per NEC rules to have serving your home. If you service size is more than minimum calculated by the link below the follow the instructions after the link.

http://www.homewiringandmore.com/hom...DmdCalc02.html

If you service size is adequate then take off your panel cover and read to ground the 120 volt rated voltage of both line one and line two of the main breaker service connections from the meter at the main breaker. Turn on the a/c unit while reading voltage on both lines separatly. If the voltage drops during strating of a/c but returns then your voltage problem is before your main service panel. Then ask the power company to open your meter base. Again test the two incoming lines if this voltage drops again inside the meter the problem is with the power company lines or transformer. You may or may not get the power company to correct if on their lines.

If you find no voltage drop showing on your voltage tester at teh main breaker when the a/c starts then suspect an undersized branch circuit conductor going to your a/c unit.

Good Luck

Wg
Reply With Quote
Reply






Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Dimming Lights correctu Electrical - Existing Home 1 November 12th, 2005 11:07 PM
Lights dimming excessively Pat the RiverRat Electrical - Existing Home 8 September 30th, 2005 02:50 PM
Dimming Lights when Water Heater Cycles Johnxa Electrical - Existing Home 12 December 29th, 2003 04:35 PM
dimming lights burnjob Electrical - Existing Home 7 October 8th, 2002 04:37 PM
Installed recessed lights etallet Building Construction - Existing Home 3 September 17th, 2002 02:15 PM


All times are GMT -4. The time now is 07:56 AM.


Powered by vBulletin® Version 3.6.7
Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.
© 2002 - QuinStreet, Inc.
http://www.selfhelpforums.com