Default Bonding bushings

I just had my inspection today for my 400A service. Passed good enough to get the stickers applied to the meter base and panel, but the inspector commented that my bonding bushings should have a locknut under them. I do have a locknut on the outside of the box, just not on the inside sandwiched between the box and the bushing. I've tried to do this in the past, but rarely are the conduit threads long enough to get that bonding bushing on far enough for my satisfaction (so the set screw fully hits threads).

So are service bonding bushings (the metal ones with a lug, set screw, and non metallic ring to protect the wires) considered inadequate to hold conduits in place? How many threads are required to engage the conduit?

I don't think the inspector is going to make me change that, it seemed more like a comment. He seemed to buy my reasoning of not enough thread. What do you guys think?
__________________
Mark
Reply With Quote
  #2   IP: 64.252.76.156
Old August 11th, 2003, 02:22 PM
Anonymous Anonymous is offline
Senior Member 'Self Help Master with Distinction'
 
Join Date: Sep 2002
Posts: 1,999
Default

You are not alone in this problem. Many connectors and often the conduit threads themselves just don't have enough for both bushing and locknut. Frustrating isn't it. If it is tight enough that the conduit is secured to the cabinet, I wouldn't worry about it, especially since everything that should be, is properly bonded.
Reply With Quote
  #3   IP: 205.188.208.70
Old August 11th, 2003, 04:47 PM
imported_Ohm1 imported_Ohm1 is offline
Senior Member
 
Join Date: Jun 2003
Posts: 255
Default Good post

We are all having that proplem, but you must have atleast three threats exposed, so you can screw your bushing on. I usually tap my nut on with my screw driver, until I can get three threats or more.
__________________
Learning brings success
Reply With Quote
  #4   IP: 148.78.243.121
Old August 11th, 2003, 08:20 PM
Wgoodrich's Avatar
Wgoodrich Wgoodrich is offline
Super Moderator

 
Join Date: Sep 2002
Posts: 7,451
Default

I can find where the conduit must be firmly secured where entering a box. I can not find anywhere it forbids metal bushings to be used to secure to a box. As far as I can find the NEC is mute on that subject other than 110.3.B calling for installation instructions to be followed. Check installation instructions, you may find your metal bushings to be listed as a securing device to boxes.

However there is a rule in 300.4 that forbids plastic bushings from being used to secure to a box.

COPIED SECTION OF NEC 2002;

300.4.F
Conduit bushings constructed wholly of insulating material shall not be used to secure a fitting or raceway. The insulating fitting or insulating material shall have a temperature rating not less than the insulation temperature rating of the installed conductors.


I find no rule against use of a bushing for securing to box. Check installation instructions to see if your bushing is listed for use as a securing device. May be there.

Trying to help

Wg
Reply With Quote
Reply






Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Bonding locknuts and concentric knockouts suemarkp Electrical Code - USA 4 February 19th, 2004 04:33 PM
Bonding water pipes and splicing. imported_archstenton Electrical - Existing Home 7 September 23rd, 2003 04:36 PM
Whats a bonding wire for? (on a gas/electronic pool heater) TRAXX Electrical - Existing Home 1 August 31st, 2003 08:14 AM
Bonding Lug on bathtub motor robomike Electrical - Existing Home 4 June 13th, 2003 02:10 AM
Pool Pump Only (no underwater lights) imported_ssabin Electrical - Existing Home 11 April 30th, 2003 05:30 PM


All times are GMT -4. The time now is 12:45 AM.


Powered by vBulletin® Version 3.6.7
Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.
© 2002 - QuinStreet, Inc.
http://www.selfhelpforums.com