I just installed some flood lights in my backyard and I ran the power source from an exisiting patio light.

I used outdoor romex and fed it through PVC conduit. Yesterday, the local home center stated that I cannot feed romex through the conduit or it will cause "sweating" and might cause a fire. Is this true?

Should I scap the PVC conduit an leave the out door romex exposed, or can I removed the romex covering and feed the electrical wires through the conduit?

Any suggestions?
  #2   IP: 12.32.197.131
Old June 30th, 2003, 09:46 AM
imported_marako imported_marako is offline
Senior Member
 
Join Date: Mar 2003
Posts: 127
Default

Technically you can't run ROMEX in conduit except for short pieces for protection (like through walls or floors).

You also technically can not simply strip the jacket of the wire and run it in the conduit (the wire is Romex are not LISTED for use).

I've never heard of Romex wire causing sweating inside conduit. Any conduit underground will "sweat" inside. Since you ran outdoor Romex (Do you mean UF??) that would suggest it is water proof, and therfore being in a "sweaty" conduit shouldn't be a problem.

Leaving romex exposed is never a good idea (weed wacker??). Personally I'd leave it as is. If you want to be to code, then you'll need to get some black, white, and green THHN/THWN wire and pull out the romex, and put this in its place.
  #3   IP: 38.164.3.135
Old June 30th, 2003, 07:05 PM
imported_Ron imported_Ron is offline
Senior Member
 
Join Date: Sep 2002
Location: New York
Posts: 364
Default

I will repectfully disagree with marako,
Article 300.5 Underground Installations: does not limit the length of cable that can be pulled through several different types of conduit for the protection of the cable.
Be sure you used UF type cable (not standard Romex or NM-b cable) so that it is rated for wet/underground installation, with or without conduit.
__________________
Ron
  #4   IP: 152.163.252.65
Old June 30th, 2003, 08:07 PM
imported_Ohm1 imported_Ohm1 is offline
Senior Member
 
Join Date: Jun 2003
Posts: 255
Default Romex

I agree with Ron. Just make sure you are using "UF" wire. Uf wire is the recognized wire for underground use-- in conduit, or not.
  #5   IP: 65.73.69.108
Old June 30th, 2003, 09:27 PM
6pack 6pack is offline
Senior Member 'Self Help Master with Distinction'
 
Join Date: Oct 2002
Posts: 1,781
Default

you also need a minimum of 18" depth when using the PVC. SCH 40 fine for underground installation.Sch 80 required above ground IF subject to damage. Haven't seen Sch 80 in most DIY centers. 24" required depth if using UF cable only and again Sch 80 PVC when leaving trench vertically to whatever.(If subject to damage)
  #6   IP: 199.245.201.5
Old July 1st, 2003, 04:51 AM
Davejgratz Davejgratz is offline
Member
 
Join Date: Nov 2002
Posts: 79
Default

The Home Depot in our area stocks both schedule 40 and schedule 80 pvc conduit. The Menards in our area also stocks both, but not quite so many sizes of the schedule 80. I suppose this varies by who runs the stores in each area,or something.

Dave
  #7   IP: 12.32.197.131
Old July 1st, 2003, 09:00 AM
imported_marako imported_marako is offline
Senior Member
 
Join Date: Mar 2003
Posts: 127
Default

OK, let me restate my answer... I rushed through the first one.

You can't install Romex in conduit.... underground (Romex = NM-B). You can install Romex in conduit above ground, or as the others have said if you use UF which is water proof, you can put it in conduit even underground.

My thought for the short peice was this: Generally running romex in coduit doesn't make sense. I belive you need to use 3/4" coduit for a single 12-2 w/g, and 1" for two peices of 12-2 w/g. This is because the width of the Romex determines to size of the conduit. So romex is about 3/8" wide. Anyway, I've seen where short peices of smaller conduit (1/2") would be used soley for protecting the romex on the way by/pass/through something.

Sorry for the confusion.
  #8   IP: 70.147.216.252
Old June 11th, 2008, 06:28 PM
diy'er diy'er is offline
Junior Member
 
Join Date: Jun 2008
Posts: 1
Default

Code lets you bury UF cable directly in the ground, but you can also run conduit the length of the trench. If you do, you wont have to bury the cable quite as deep-12 inches instead of 24 inches as with the UF- in residential applications. You will, however, have to fish cable through the conduit. Contrary to what you may read on these forums running UF or other cable through conduit DOES meet code, but cable adds expense and the sheathing may make it difficult to fish. Most electricians feed three single wires, known as TW wires, through the conduit instead. If you do this run the conduit first, and glue the sections together if your dealing with PVC conduit. If your working with metal conduit besure to use compression fittings made specifically to keep water out. Once the conduit is in place, fish all three wires at once.
  #9   IP: 76.104.172.149
Old June 11th, 2008, 07:43 PM
suemarkp suemarkp is offline
Super Moderator

 
Join Date: Dec 2003
Location: Kent, WA
Posts: 8,123
Default

You can only bury at 12" if the wire is breakered at 20A or less and it has GFCI protection before entering the earth. Conduit would allow the burial depth of direct bury cable to be reduced from 24" to 18" in most other cases.
__________________
Mark
Kent, WA
  #10   IP: 209.91.39.169
Old June 11th, 2008, 09:12 PM
Ohm1's Avatar
Ohm1 Ohm1 is offline
First Class Moderator

 
Join Date: Dec 2003
Location: WA
Posts: 4,628
Default

How did this old tread get re-born. I'm temped to close this tread!
__________________
Learning brings success. While you are waiting, I'm getting better!
Closed Thread






Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Split oven/stove wiring Tom L. Building Construction - Existing Home 15 May 23rd, 2009 01:43 PM
Running NM in PVC Outside Unregistered Electrical Code - USA 22 November 14th, 2004 06:00 PM
Ground Lineman Electrical - Existing Home 4 December 15th, 2002 07:02 PM
220 Circuit Help Dave Sveden Electrical - Existing Home 3 December 14th, 2002 03:20 PM
extending a 3-wire circuit glw Electrical - Existing Home 1 October 24th, 2002 03:14 PM


All times are GMT -4. The time now is 06:59 AM.


Powered by vBulletin® Version 3.6.7
Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.
© 2002 - QuinStreet, Inc.
http://www.selfhelpforums.com