IP: 209.179.245.156
May 14th, 2003, 10:38 PM
rayb
Junior Member
Join Date: May 2003
Posts: 10
Reuse 240V Dryer Circuit?
I have a question about 240 volt dryer circuits. I apologize if this is a duplicate topic as I just found the site and forums and was unable to find any matches.
I have an unused 240V dryer circuit in my garage (we got a gas dryer and it only required 120V). I would like to save some time, money and sweat to add some power to my garage using this circuit. It is currently made up of 3 wires, look like 10AWG copper, pulled through buried conduit from a double-pole? (2 toggles tied together) 30 AMP breaker in my main panel.
My main question is, what would be the best way to use the existine wires to power an air compressor that requires a 240V Single-phase receptacle?
Secondly, is there a safe, legal way to use the same wiring to
rayb
View Public Profile
Find all posts by rayb
#
2
IP: 65.73.69.87
May 14th, 2003, 11:10 PM
6pack
Senior Member 'Self Help Master with Distinction'
Join Date: Oct 2002
Posts: 1,736
To get started, I would repost if garage is attached to house or seperate from house. Entire different set of code rules for either or. Not sure if underground wiring was only way to get to attached garage or seperate run to unattached garage.While at it if seperate garage tell us if also general wiring out there for lights and general outlets? Also post the amperage draw of compressor mentioned.Also size of conduit and type(thinwall, ridgid, IMC.) Need this info to help in your answer, numerous solutions may be available to you. GL
6pack
View Public Profile
Send a private message to 6pack
Find all posts by 6pack
#
3
IP: 209.179.245.156
May 14th, 2003, 11:15 PM
rayb
Junior Member
Join Date: May 2003
Posts: 10
Oops. I think I may have found my answer. I ran across the
220 subpanel for compressor
post by
bchase
and realized this would probably work for me as well. I would like to confirm though, if I upgrade the breaker at the main panel to a 50 AMP and then install a subpanel in the garage (around 75-100 feet away) with a 220 breaker for the compressor circuit and a 110 for the lights and some outlets, I would be allright.
If I run the subpanel this way, what about the neutral return from the 110 circuit? Would it just tie to the subpanel's neutal buss? Would it be right for the neutral and ground to be tied together at the subpanel? I want to be lazy but I also want to be safe.
Thanks again...Ray
rayb
View Public Profile
Find all posts by rayb
#
4
IP: 209.179.245.156
May 15th, 2003, 12:02 AM
rayb
Junior Member
Join Date: May 2003
Posts: 10
More Detail
I'll do the best I can. Wiring was here when I bought the house. the garage is attached and the plugs and light in the garage are all wired from the house.
I presume it was run after construction as it is run from the service panel through a hole in the stucco below the panel into the conduit and then underground. If I am understanding the conduit types correctly, it believe it is 1/2" ridgid conduit (thicker walled from the panel to the entry through the garage wall, then run in thinwall from there to the dryer plug.
I couldn't find the exact current load on the compressor but the manual did say that it could be wired to a 15 AMP circuit providing it was "dedicated" with no other loads on the line. I figured on a 20 AMP anyway just to be safe.
Quote:
Originally Posted by
wannabee
To get started, I would repost if garage is attached to house or seperate from house. Entire different set of code rules for either or. Not sure if underground wiring was only way to get to attached garage or seperate run to unattached garage.While at it if seperate garage tell us if also general wiring out there for lights and general outlets? Also post the amperage draw of compressor mentioned.Also size of conduit and type(thinwall, ridgid, IMC.) Need this info to help in your answer, numerous solutions may be available to you. GL
I can guess where you are going with the question of outlets and ligts already there. I had originally planned on just extending the existing circuit but it's already loaded pretty well. I extended the existing single light circuit to serve 4 flourescent shop lights and an outlet for a chest freezer and refrigerator. It also serves the lights to the master bedroom and bath next door and the lights dim when the freezer fires up, hence my desire to include another circuit for either lights or the appliances.
There's also an outlet that is currently running the washer and gas dryer. I could extend this for more plugs but adding the freezer and fridge to this one (along with the 4 plugs in the house on the same circuit) likely wouldn't gain me much.
Hope that's enough. I look forward to your help.
Ray
rayb
View Public Profile
Find all posts by rayb
#
5
IP: 207.35.6.2
May 15th, 2003, 06:29 AM
imported_joed
Senior Member
Join Date: Jan 2003
Location: welland ontario
Posts: 372
If the wire is # 10 you can not upgrade the breaker to 50 amp. You must leave it at 30 amp. If the cable only has 3 wires then you can't use it as a sub panel. You need a black, white, red and bare ground to make a sub panel.
You can change the receptacle to a 30 amp receptacle to match your compressor and use it. Your compressor will not require 110 so a 3 wire cable will work fine for that.
imported_joed
View Public Profile
Send a private message to imported_joed
Find all posts by imported_joed
#
6
IP: 12.28.136.3
May 15th, 2003, 08:50 AM
rayb
Junior Member
Join Date: May 2003
Posts: 10
Quote:
Originally Posted by
joed
If the wire is # 10 you can not upgrade the breaker to 50 amp. You must leave it at 30 amp.
Is this because #10 wire cannot carry more than 30 amps? If so, what size wire and breaker would I need to effectively feed a 20 amp circuit for the compressor and another 15 amp 110 circuit for lights and plugs (assuming I pull a fourth wire to provide the proper grounding for a subpanel)?
Thanks again.
rayb
View Public Profile
Find all posts by rayb
#
7
IP: 65.73.69.113
May 15th, 2003, 02:12 PM
6pack
Senior Member 'Self Help Master with Distinction'
Join Date: Oct 2002
Posts: 1,736
You said this is attached garage! You also said wire run in conduit? You also said appears to be ridgid. The ridgid pipe would be your ground. Depending on U/G pipe run(condition and # of bends) not sure if you can pull another pair of #12 in with that existing circuit,if so you would be set.Not sure how NEC looks at this when existing. Again if legal(pipe fill). Might even be able to install a six circuit panel fed by that #10 with 30A D/P protection. Lets see what WG has for you on this. Need to know exactly amp draw on that compressor. Hang in there till later.
6pack
View Public Profile
Send a private message to 6pack
Find all posts by 6pack
#
8
IP: 12.28.136.3
May 15th, 2003, 02:27 PM
rayb
Junior Member
Join Date: May 2003
Posts: 10
[quote="wannabee"]Need to know exactly amp draw on that compressor. quote]
I'll look at the compressor again tonight and post the draw. I honestly appreciate all the help.
The pipe looks in good condition, appears to only have 4 bends (estimating 2 below ground). As to pulling more wire, I think I shouldn't have any problem getting another 2 #12 wires through. It would be tight with romex but the single, solid core (like is in there now) would fit fine.
Look forward to your input.
rayb
View Public Profile
Find all posts by rayb
#
9
IP: 206.100.220.195
May 15th, 2003, 10:10 PM
Mark_R
Member
Join Date: Jan 2003
Location: Nevada, USA
Posts: 34
Ray,
Take a thorough look at
http://www.homewiringandmore.com/hom...rageshowp.html
provided by the good folks that run this site. There's a lot if information there to digest, so I'd suggest printing it out for review. If the link gets broken in the post, write it down and type in into your browser manually.
Also note that "tight with romex" (or single core wire) is not a good thing... there are valid engineering concepts (building codes) that prevent those 'pipes' from being stuffed with too many wires, for your and others safety....
Mark_R
View Public Profile
Send a private message to Mark_R
Find all posts by Mark_R
#
10
IP: 209.178.130.40
May 18th, 2003, 10:20 PM
rayb
Junior Member
Join Date: May 2003
Posts: 10
Ok. I was able to find out the current draw on the compressor motor. It pulls 13.1 amps. I anxiously await your recommendations.
Ray
rayb
View Public Profile
Find all posts by rayb
Page 1 of 2
1
2
>
«
Previous Thread
|
Next Thread
»
Currently Active Users Viewing This Thread: 1
(0 members and 1 guests)
Thread Tools
Show Printable Version
Email this Page
Display Modes
Linear Mode
Switch to Hybrid Mode
Switch to Threaded Mode
Posting Rules
You
may not
post new threads
You
may not
post replies
You
may not
post attachments
You
may not
edit your posts
vB code
is
On
Smilies
are
On
[IMG]
code is
On
HTML code is
Off
Forum Jump
User Control Panel
Private Messages
Subscriptions
Who's Online
Search Forums
Forums Home
Building
Building Codes - Commercial
Building Codes - Residential
Electrical Code - CANADIAN
Electrical Code - USA
Plumbing Codes - Residential
Electrical Examinations & Brag Board Category
Brag Forum
Electrical Exam Preparations
Environment
Septic Systems
Water Quality
Horror Section
Construction Horror Stories
Wall of Shame
New Home, 'Planning a New Home'
New Homes - Building from the Ground Up
Outdoors, 'The Great Outdoors'
Camping
Firewood
Freshwater Fishing
Hunting & Tracking
Stories about The Great Outdoors
Yard & Garden
Repair
Appliance Repair
APPLIANCE AID SITE
Automotive
Boats
Building Construction - Existing Home
Computers & Data Wiring
Electrical - Existing Home
Electrical = Industrial / Commercial/Power Distribution
Energy Savings & Envelope Blanket of Structure - Existing Home
Heating & Air Conditioning - Existing Home
Home Security
Interference
Plumbing - Existing Home
Small Engines
Small Engines
Telephone Wiring
The Tool Shed
Suggestions & Help
Help on Using Our Site or Forums
Site Server Issues / Problems
Suggestions
Test Forum
Tips & Hints / Non - Interactive Forum Category
Appliances - Tips & Hints - NO QUESTIONS FOR HELP HERE
Electrical - Tips & Hints - NO QUESTIONS FOR HELP HERE
Plumbing - Tips & Hints - NO QUESTIONS FOR HELP HERE
Similar Threads
Thread
Thread Starter
Forum
Replies
Last Post
Dryer Circuit Kicking Off - Need to solve the puzzle.
clm
Electrical Code - USA
5
August 7th, 2006
07:53 AM
Dryer Circuit Kicking Off - Need to solve the puzzle
clm
Appliance Repair
5
August 6th, 2006
02:13 PM
No power to dryer, is it the circuit breaker?
ed team
Electrical - Existing Home
1
September 28th, 2005
06:34 PM
120V multiple outlets from a 240V dryer outlet for temp computer use.
Dude
Electrical - Existing Home
20
August 20th, 2004
01:16 PM
dimming lights
burnjob
Electrical - Existing Home
7
October 8th, 2002
04:37 PM
All times are GMT -4. The time now is
09:35 PM
.
Contact Us
-
Self Help and More
-
Archive
-
Top
Powered by vBulletin® Version 3.6.7
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.
(c) 2010 Self Help and More 'All Rights Reserved'
http://www.selfhelpforums.com