I have to replace the pipe from the meter to house since its currently steel and 42 years old. The county said I need to use copper. .

The meter to the house distance is 72 feet, the meter is sized for 3/4" fittings, the current pipe is also 3/4", and the house has been recently piped all in 3/4" copper. Water presure is 44 PSI at the entrance to the house. I did get to see the inside of the steel pie and its internal size has been reduced a lot by gunk all in side.

A plumber at the parts counter said to use 1". He could not explain why it would work better, but said he had done this before for his company many times. Another jumped in and said it had to do with sidewall resistence. I find it would be harder for the water to push from 3/4" to 1" then back down to 3/4" when it enters the house.

The question is what size pipe should I use for the best flow and pressure? I will be using 20' lengths of copper.

By the way. If a 1" or larger pipe is required should the house have been plumbed with the same for best performance.

Thanks for your help,

Tom
Reply With Quote
  #2   IP: 148.78.243.122
Old March 25th, 2003, 05:38 PM
Wgoodrich's Avatar
Wgoodrich Wgoodrich is offline
Super Moderator

 
Join Date: Sep 2002
Posts: 7,115
Default

The supply line is sized by the load applied much like electricity is done. Depends on how many and what type outlets you have in your home. List all types of faucets, hose bibs, etc. in your home then we can size the minimum size required to serve your home as your water supply line.

The answers you have been getting sounds like they are by the seat of the pants, experience guesses. The supply line is supposed to be sized by the number and type of faucet outlets etc. Don't forget to name washers, dishwashers etc. also.

Then we can calculate the pipe size you require.

Good Luck

Wg
Reply With Quote
  #3   IP: 67.34.46.199
Old March 26th, 2003, 07:20 AM
Anonymous Anonymous is offline
Senior Member 'Self Help Master with Distinction'
 
Join Date: Sep 2002
Posts: 1,999
Default Missing answers

Thanks for your quick reply. I have the following,

5 hose bibs
1 washer
2 vanity sinks
1 kitchen sink
I dishwasher
2 showers.
2 toilets

I will be adding two hose bibs, not that I use them at the same time but are for convienence (don't like dragging a long hose around). The bibs will be along the existing pipe run if that makes a difference.

I hope this is the correct information.

Tom
Reply With Quote
  #4   IP: 148.78.243.121
Old March 26th, 2003, 02:39 PM
Wgoodrich's Avatar
Wgoodrich Wgoodrich is offline
Super Moderator

 
Join Date: Sep 2002
Posts: 7,115
Default

YOU SAID; 75 FEET METER FITTING SIZE 3/4" @ 44 psi;
5 hose bibs
1 washer
2 vanity sinks
1 kitchen sink
I dishwasher
2 showers.
2 toilets

Chart 2903.7 IRC
The maximum plumbing units allowed with the meter, fittings, pressure, distance using 3/4" supply line to your house would allow

8.5 plumbing units.

Chart P2903.6 IRC 1.4 per bath group, 1.4 washer, 2.5 kitchen group, 2.5 hose bibs totalling 7.8 total plumbing units.

You are allowed a maximum of 8.5 plumbing units, you have with one hose bib total 7.8 plubing units.

As long as you are not using a sprinkle system you are within minimum supply line size using 3/4" as you discribed. However if you plan on running more than one hose bib or have a sprinkler system then you need the 1" supply line to the house.

Remember just one short piece of pipe reducing smaller than the rest of the pipe limits that pipe supply rating to the smallest fitting in your system. Also understand that the feeder along the street while serving more than one house also is calculated in a different manner giving diversification of not all house using all fixtures at same timel. Don't worry about what the Utility supplies you and your supply line being bigger. This is not uncommon.

Hope this helps

Wg
Reply With Quote
  #5   IP: 68.83.12.178
Old March 26th, 2003, 07:11 PM
Anonymous Anonymous is offline
Senior Member 'Self Help Master with Distinction'
 
Join Date: Sep 2002
Posts: 1,999
Default

You can get your 1'' copper (K) in soft rolled . This will allow to have a continous piece without joints. which could be potential problems in the future.
Reply With Quote
  #6   IP: 12.94.44.88
Old March 27th, 2003, 04:55 PM
Anonymous Anonymous is offline
Senior Member 'Self Help Master with Distinction'
 
Join Date: Sep 2002
Posts: 1,999
Default Potential problems

A plumber at the parts counter sugested to use a roll of copper in order to avoid joints and the pressure drop they cause.

When you say problems do you mean from improper soldered joints causing a problem? I read on the copper asosiation site that a joint that wasn't debured could cause a sort of small eddy (disrupt flow) and cause corrosion in the pipe to a point of failure.

Tom
Reply With Quote
  #7   IP: 148.78.243.123
Old March 27th, 2003, 05:55 PM
Wgoodrich's Avatar
Wgoodrich Wgoodrich is offline
Super Moderator

 
Join Date: Sep 2002
Posts: 7,115
Default

The bur is supposed to be removed for that reason.

Wg
Reply With Quote
Reply






Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Modine heater size and pipe size Bill Brescia Heating & Air Conditioning - Existing Home 4 May 19th, 2008 10:12 AM
Size of drain pipe for toilet and sink woodworker2000 Building Codes - Residential 6 March 30th, 2006 09:03 PM
150' run to pool pump from house, what size wire? fg4432 Electrical Code - USA 1 March 30th, 2006 02:52 PM
Gas pipe size dshaf Plumbing Codes - Residential 2 January 3rd, 2006 09:32 AM
New Service *JOHNNY Electrical - Existing Home 0 December 12th, 2003 11:36 AM


All times are GMT -4. The time now is 03:17 AM.


Powered by vBulletin® Version 3.6.7
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
(c) 2008 Self Help and More 'All Rights Reserved'
http://www.selfhelpforums.com