Default How does one measure the voltage on a 230v 3 phase line?

Gentelmen:

I'm installing a 230v 3 phase (phase sensitive) heat pump unit how does one measure the voltage, across L1-L3 or L1-L2???. The unit is a Florida Heat Pump model em 096. Directions state that the unit is wired 230 but if service is 208v we must move a wire over (provided in panel in ac unit.) Does anyone have any experience with this type of a unit.

Thanks

Tom
Reply With Quote
  #2   IP: 148.78.243.122
Old February 23rd, 2003, 08:36 AM
Wgoodrich's Avatar
Wgoodrich Wgoodrich is offline
Super Moderator

 
Join Date: Sep 2002
Posts: 7,451
Default

You need to be careful concerning what type three phase you are being served.

208/110
240 only
240 corner grounded
240 hot leg
480/277
480 only


There are many different types of three phase. Open you main service rated panel. Look to see if you have a neutral bare and four wires coming in from utility company.

If only three wire service you need to test from phase 1 to phase 2 then phase 2 to phase 3 then phase 3 to phase 1. Then test from each phase to your equipment grounding conductor separately.

If with four wire service you need to test from phase 1 to phase 2 then phase 2 to phase 3 then phase 3 to phase 1 then each phase to the neutral bar separately.

Tell us the voltages you find in each test then we should be able to tell you if delta or wye or wye/delta or hot leg or corner grounded delta or open delta service.

Then you can adjust your a/c unit to match your type three phase service supplied.

Curious

Wg
Reply With Quote
  #3   IP: 97.81.213.69
Old February 7th, 2008, 08:38 AM
ceramicbrad ceramicbrad is offline
Junior Member
 
Join Date: Feb 2008
Posts: 5
Post

Quote:
Originally Posted by Wgoodrich View Post
You need to be careful concerning what type three phase you are being served.

208/110
240 only
240 corner grounded
240 hot leg
480/277
480 only

Tell us the voltages you find in each test then we should be able to tell you if delta or wye or wye/delta or hot leg or corner grounded delta or open delta service.


Wg
This was an interesting post. Too bad anonymous decided not to follow up and answer the above question yet posted many others after this.

Confused:
Reply With Quote
  #4   IP: 24.172.159.98
Old March 7th, 2008, 10:32 AM
StanL StanL is offline
Junior Member
 
Join Date: Mar 2008
Posts: 2
Default How does one measure the voltage on a 230V 3 Phase Line?

I've read this post and would like an answer to my voltages on what type of outputs they are, Wye, Delta, Star...?

I read the following:
L1-L2 = 236VAC
L2-L3 = 234VAC
L1-L3 = 240VAC
L1-N = 118
L2-N = 118
L3-N = 205

L3-N looks excessive...


Thanks
Stan
Reply With Quote
  #5   IP: 76.104.172.149
Old March 7th, 2008, 10:42 AM
suemarkp suemarkp is offline
Super Moderator

 
Join Date: Dec 2003
Location: Kent, WA
Posts: 8,261
Default

This is 240V delta. The one leg on this is "special" as you noticed and is called the high leg. It is typically 208V to ground and it not used by itself. To help ensure you don't accidently use it for 120V loads, that wire is supposed to be colored orange. Sometimes this orange colored wire is required to be in a specific position in a meter or panelboard. Even if you have a single phase 208V load to run from it, I don't think the transformers likes it being used (may overload them). The high leg should only be used in circuit that need all 3 phases.

On 240V delta, one side of the triangle provides "normal" house power -- 240V from the ends, and 120V from those ends to the center tap (which is where the neutral is). You use all 3 corners in a 3 phase load. Most delta 3-phase doesn't use the neutral, but there is still a grounding wire in all circuits and feeders which goes to that neutral point anyway.
__________________
Mark
Kent, WA
Reply With Quote
  #6   IP: 24.150.120.191
Old March 7th, 2008, 06:44 PM
Homer's Avatar
Homer Homer is offline
Senior Member with Distinction
 
Join Date: Dec 2003
Location: Springfield
Posts: 947
Send a message via AIM to Homer
Default

Since a pic is worth a thousand words, here's a 4-wire Delta transformer secondary.

B is the high leg in this pic.

The "high", or "wild" or "crazy" leg is supposed to be colored orange in the US.

Homer
Attached Thumbnails
Click image for larger version

Name:	delta_cntrgrnd.gif
Views:	73
Size:	2.8 KB
ID:	2010  
__________________
Depending on your skills, doing your own electrical work may risk the health and safety of the community. Always find out how to do things safely before beginning.
Reply With Quote
  #7   IP: 24.172.159.98
Old March 10th, 2008, 10:22 AM
StanL StanL is offline
Junior Member
 
Join Date: Mar 2008
Posts: 2
Default

Thanks for the quick answers. Now I know I can use this source for the power supply testing I need to do.

Thanks again,
Stan
Reply With Quote
  #8   IP: 74.61.10.251
Old November 2nd, 2011, 12:35 AM
jammer jammer is offline
Junior Member
 
Join Date: Nov 2011
Posts: 1
Default do mine, do mine

This is a great thread started, although a bit old.
I found it by google - and so far I can not find anywhere else that has examples to identify types of 3 phase.

I am setting up a machinists mill that came with a variable frequency drive, but it is 3ph 380-460v and I have 220 3ph, so I am looking for a transformer.

In calculating transformers I have found you need to know the type of 3phase.

My 3ph measures:
L1-L2 = 212VAC
L2-L3 = 212VAC
L1-L3 = 213VAC
L1-N = 122
L2-N = 123
L3-N = 121

After reading for many hours, I believe I have a good grasp on 3phase, just a workout understanding all the types, I have found no less then 8 different types. The difference in Wye vs Delta and combinations of the two.....sheesh.

What really baffles me is trying to apply a correct transformer, understanding KVA, yet factoring in the coil ratio. The problem I have is trying to obtain the specs from manufactures is difficult.

Probably end up getting a 220-240 VFD.

any help would be electrifying
Reply With Quote
  #9   IP: 207.35.6.2
Old November 2nd, 2011, 06:32 AM
joed's Avatar
joed joed is offline
Super Moderator

 
Join Date: Dec 2003
Location: Welland Ontario
Posts: 4,646
Default

You shouldn't need to be concerned about coil ratio. Input voltage, output voltage, KVA and delta or wye are you concerns.
Reply With Quote
  #10   IP: 24.18.116.5
Old November 2nd, 2011, 12:39 PM
suemarkp suemarkp is offline
Super Moderator

 
Join Date: Dec 2003
Location: Kent, WA
Posts: 8,261
Default

You have 208Y 3-phase. You can change from wye to delta if you want via the transformer. Just depends on whether that mill needs a neutral or it just uses 3 phase wires. I also don't believe there is a problem powering a delta load from a wye source (as long as the voltages match). The main consideration is if you will have other 480V things in your future that may need wye, or if you need 277V volts for something.
__________________
Mark
Kent, WA
Reply With Quote
Reply






Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
HELP... Pool Bonding Grid System for Above Ground Pool. syburr Electrical - Existing Home 14 May 27th, 2011 08:19 AM
motor kilowatts dewayne Electrical = Industrial / Commercial/Power Distribution 15 March 21st, 2006 09:47 PM
Line voltage thermostat puzzle mdshunk Heating & Air Conditioning - Existing Home 4 January 29th, 2004 06:25 PM
Ac Voltage On Phone Line! *SILVERSLAB Telephone Wiring 0 December 11th, 2003 12:40 PM
120v vs 220v lighting Anonymous Electrical - Existing Home 1 November 24th, 2002 10:36 AM


All times are GMT -4. The time now is 08:17 PM.


Powered by vBulletin® Version 3.6.7
Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.
© 2002 - QuinStreet, Inc.
http://www.selfhelpforums.com