Default 15 amp outlets and 20 AMp breaker

Is this allowable. I am finishing my basement. I have a few packages of standard home 15 amp outlets, I am wondering if a 15 amp outlets are allowable to hook to a 20 amp circuit braker in the service panel. I plan on doing nothing more than plugging in veryday equipt to these. TV stereo etc. No shop tools, pumps, motors...etc. just plain ol outlets. I have a book that states that the outlets should be apropriate for the amperage of the circuit but doesn't specify what that means. The wiring is a 12/2 gauge. My upstairs was done by professional contractors and they hooked 15 amp outlets to 20 amp breakers but I still need to know. Thanks.
Reply With Quote
  #2   IP: 207.35.6.2
Old February 21st, 2003, 10:56 AM
imported_joed imported_joed is offline
Senior Member
 
Join Date: Jan 2003
Location: welland ontario
Posts: 372
Default

Yes it is permissable to use 15 amp outlets on a 20 amp circuit.
Reply With Quote
  #3   IP: 206.148.224.212
Old February 23rd, 2003, 10:22 PM
imported_ssabin imported_ssabin is offline
Member
 
Join Date: Sep 2002
Location: MI
Posts: 79
Default

Only time you can't do that is if a single receptacle is on the circuit.

You're fine if you're using duplex receptacles.
__________________
Scott Sabin
Reply With Quote
  #4   IP: 66.222.103.18
Old February 23rd, 2003, 11:01 PM
casey casey is offline
Member
 
Join Date: Feb 2003
Location: Wisconsin, USA
Posts: 59
Default

Quote:
Originally Posted by ssabin
Only time you can't do that is if a single receptacle is on the circuit.
Does this mean that if a single receptacle is anywhere on the circuit, the rest of the receptacles must have a matching amp rating?
Reply With Quote
  #5   IP: 148.78.243.122
Old February 24th, 2003, 04:41 PM
Wgoodrich's Avatar
Wgoodrich Wgoodrich is offline
Super Moderator

 
Join Date: Sep 2002
Posts: 7,451
Default

I suspect you may have misunderstood what ssabin meant to say. A dedicated branch circuit with a single hole receptacle must be rated equal to the amp rating of that dedicated branch circuit.

If you have a branch circuit with multiple single hole receptacles in that branch circuit then you have a branch circuit where you could install 15 or 20 amp single receptacles in that 20 amp rated multioutlet branch circuit.

SSabin was referring to a dedicated circuit with a single outlet serving a dedicated load, not a multioutlet branch circuit. At least this is what I think he meant to say.

Also it is a Code violation to install 20 amp receptacle or receptacles whether single or duplex on a 15 amp 14 awg branch circuit.



Hope this helps

Wg
Reply With Quote
  #6   IP: 66.222.103.169
Old February 24th, 2003, 06:43 PM
casey casey is offline
Member
 
Join Date: Feb 2003
Location: Wisconsin, USA
Posts: 59
Default

Should have thought of "single" and "singleplex" meaning different things.

Let's see if I have this right .

If the circuit is dedicated (has only one outlet), the amps must match, period.

On a 20 amp circuit with multiple receptacles, I can mix and match 15 and 20 amp outlets, either singleplex or duplex, to my heart's content.

On a 15 amp circuit with multiple receptacles, I can use any combination of singleplex and duplex receptacles as long as they're designed for a 15 amp circuit.

How am I doing?
Reply With Quote
  #7   IP: 148.78.243.122
Old February 24th, 2003, 07:08 PM
Wgoodrich's Avatar
Wgoodrich Wgoodrich is offline
Super Moderator

 
Join Date: Sep 2002
Posts: 7,451
Default

NEC 2002

210.21.B
(B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit. A single receptacle installed on an individual branch circuit shall have an ampere rating not less than that of the branch circuit.

(3) Receptacle Ratings. Where connected to a branch circuit supplying two or more receptacles or outlets, receptacle ratings shall conform to the values listed in Table 210.21(B)(3),


The table say not to exceed 15 amp receptacles on a multioutlet branch circuit rated for 15 amps maximum wire or breaker size.

15 or 20 amp receptacles allowed on a multioutlet branch circuit rated for 20 amp maximum wire or breaker size.

The NEC does not care if single plug receptacle or duplex receptacle. The NEC only cares that a dedicated circuit with only one load or outlet must be a receptacle rated in amps equal to teh amp rating of that dedicated branch circuit serving only one utilization equipment.

Hope this helps

Wg
Reply With Quote
Reply






Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Breaker Panel Questions QueenBee Electrical Code - USA 10 December 6th, 2006 03:11 PM
Power at breaker but none at outlets Jesse Electrical - Existing Home 8 November 12th, 2006 02:28 PM
Partial Wall Outlets Not working on Same Breaker Unregistered Electrical - Existing Home 7 June 16th, 2005 06:46 PM
How many outlets and switches to each breaker? Unregistered Electrical Code - USA 11 May 1st, 2005 07:44 AM
Bad Circuit Breaker? *Guest Electrical - Existing Home 0 December 12th, 2003 11:34 AM


All times are GMT -4. The time now is 04:43 AM.


Powered by vBulletin® Version 3.6.7
Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.
© 2002 - QuinStreet, Inc.
http://www.selfhelpforums.com