Default Hot/Ground Reversed

This is existing wiring and has not been modified in years. Monday several outlets on the circuit stopped working, while others still worked fine.
It did not trip the breaker. I used a tester. Working outlets showed correct. Failed outlets show hot/ground reversed. Tuesday, I went to troubleshoot the problem and all outlets were working and tested correct. I did the following: Since the wiring strings from outlet to outlet, I went to the last working outlet, (on Monday), and inspected the connections. The wires were pushed in the back of the outlet and not screwed onto the outlet, and the neutral wire going to the next outlets in line was barely in the hole. I attached all wires to the screws. I also checked all other outlets and removed wires from rear holes and also attached them to the screws. I checked a junction box which feeds some outlets and retightened the wire nuts and taped. I used the tester again and all test fine. I used a meter, and tested ground, neutral to hot = 120 V, hot to ground = 120 V, neutral to ground 0 V. I also replaced the breaker.
Questions:
In your opinion does it appear to have been a loose neutral wire ?
Is there anything else I can / should check ?

thx, Mark
Reply With Quote
  #2   IP: 136.1.1.101
Old July 13th, 2005, 08:14 AM
Roger's Avatar
Roger Roger is offline
Senior Member 'Self Help Master with Distinction'
 
Join Date: Aug 2004
Location: Kansas
Posts: 1,585
Default

Yes you had a bad neutral connection or open due to those backstabbed outlets. These are notorious for this problem. You did the right thing moving the wires to the screws. When you use those outlet testers and the lights tell you that you have a hot/ground reverse this really is a open neutral indication. When you think about it getting the ground and hot connections reversed would be pretty darn hard to do, especially when you had a working circuit and then it stops working and you havent touched a thing. There are some people that think there are little green creatures running around in your wiring messing with you. The reason you get this hot/ground reverse as I understand is that with other loads plugged in to the circuit...lights, battery chargers etc when your neutral opens somewhere in the circuit you can actully read 120 volts from neutral to ground from backfeed through these other loads on the circuit. Your tester sees that voltage and indicates you have a hot/ground reverse. If you unplug all the loads on the circuit and unscrew the light bulbs and prevent this backfeed then the tester will change to an open neutral indication. Does this make sense to you?

Last edited by Roger : July 13th, 2005 at 08:43 AM. Reason: Spelling
Reply With Quote
  #3   IP: 12.111.220.126
Old July 13th, 2005, 08:31 AM
mcarrio mcarrio is offline
Junior Member
 
Join Date: Jul 2005
Posts: 5
Default

Thanks very much for your input. I understand what you are saying. I figured I was on the right track, but I wanted to here it from someone who knows about these things. This site was suggested from a co-worker. Great site !

thx, again, Mark
Reply With Quote
  #4   IP: 65.11.69.233
Old February 16th, 2008, 02:40 AM
SuperNinja SuperNinja is offline
Junior Member
 
Join Date: Feb 2008
Posts: 1
Default

Thanks for the info, mcarrio and Roger.

I had the same problem today.
I messed around with trying to find the correct circuit breaker, and metering individual breakers, and pretty much wasting time.

So I did a search on the internet and found this thread, and using the info you posted, I was able to quickly find the source of the problem. (One outlet that had bad connections, wires plugged into the back of the outlet)

I moved the wires over to the screws, and everything worked fine after that.





Edit:
Looks like I spoke too soon.
The problem came back today, after a hair dryer was used on the circuit.
The hair dryer works ok on other circuits though.

Last edited by SuperNinja : February 16th, 2008 at 05:08 PM.
Reply With Quote
  #5   IP: 71.60.58.53
Old August 23rd, 2009, 07:42 AM
Shontzy Shontzy is offline
Junior Member
 
Join Date: Aug 2009
Posts: 1
Default Thanks! Hot/Ground Reversed = Open Neutral

Quote:
Originally Posted by Roger View Post
The reason you get this hot/ground reverse as I understand is that with other loads plugged in to the circuit...lights, battery chargers etc when your neutral opens somewhere in the circuit you can actully read 120 volts from neutral to ground from backfeed through these other loads on the circuit. Your tester sees that voltage and indicates you have a hot/ground reverse. If you unplug all the loads on the circuit and unscrew the light bulbs and prevent this backfeed then the tester will change to an open neutral indication. Does this make sense to you?

Thanks a lot for this explanation. I was working on a sudden problem at my house for a LONG time and could not understand how the hot and ground could have gotten reversed. This really just means there is an open Neutral (white wire) somewhere on the circuit. When you have another area of the circuit with a load, that's when it would read hot/ground reverse. I had a light switch on the circuit, and when the light was "on" (the lights weren't working but there was power) the tester read "hot/ground reverse". When the light was off, it just read open neutral which was the correct reading.

To fix this problem, find the first outlet on the circuit that DOES work and make sure the neutral wire is properly connected. (The problem will either be with the first one that does work, or the first one that doesn't work which you have probably already checked at this point.) For me, this outlet worked but the neutral wire going to the rest of the circuit was loose so none of the other wires on the circuit worked. Once I tightened the wire, everything came back on.
Reply With Quote
  #6   IP: 24.252.192.57
Old October 31st, 2009, 02:30 PM
flyrobert flyrobert is offline
Junior Member
 
Join Date: Oct 2009
Posts: 1
Smile Great info

great Info the same thing happend to me, I took of every outlet cover {5} and ceiling fixture even my outside lights all tested and all showed up as hot/ground reversed, came across this site, and wa-la I went to the only outlet that worked on the same circut. i would have never looked at that outlet, my next step was an electrician, on a saturday holloween day, $125.00 just to come out ouch... . ., and sure enought the ground wire was look it just fell out when i took the recepticle out and screwed it to the switch
and working lights
Thanks so much........
Reply With Quote
Reply






Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Hot/Grnd Reversed? AntAus Electrical - Existing Home 4 October 6th, 2006 05:41 PM
ground and hot reversed *Amir Electrical - Existing Home 0 December 12th, 2003 11:45 AM
Hot/Ground wiring is reversed Anonymous Electrical - Existing Home 9 September 11th, 2003 11:44 AM
main house power source may be reversed? mikeandwes Electrical - Existing Home 2 November 7th, 2002 04:34 PM


All times are GMT -4. The time now is 06:15 AM.


Powered by vBulletin® Version 3.6.7
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.
(c) 2008 Self Help and More 'All Rights Reserved'
http://www.selfhelpforums.com