Grounding subpanel?
Now have run 3 wire and ground to a detached garage (PVC) and wondering what the correct method is for bonding the panel to earth (ground rod or water pipes)? Is there a standard fitting for exiting the service panel/exterior wall with the ground wire to the ground rod? Instead of using a ground rod can I bond to the water pipes? Is this also to be done outside the dwelling? Water pipes are a fair distance from the house where the wiring to the garage originates.
Unregistered
#
2
IP: 24.16.225.236
July 7th, 2005, 07:42 PM
suemarkp
Super Moderator
Join Date: Dec 2003
Location: Kent, WA
Posts: 7,798
Since you ran 4 wires (two hots, a neutral, and a grounding wire), you do the following:
DO NOT install the green bonding screw to the neutral bar -- it must remain electrically isolated from the panel. Install the white wire in your feeder here.
Buy an accessory ground bar for your panel if it didn't come with one and screw it to the panel chassis. The green or bare grounding wire in your feeder goes to this bar.
Install at least one ground rod, and maybe two. You have to have these even if you have a metal water pipe ground. The ground electrode conductor also goes to the ground bar in the subpanel. You can just drill a hole in the wall (angling downward) and run the ground wire through it, or do it nicer by installing a 1/2" PVC LB fitting and a length of PVC conduit down to the dirt.
I'm confused with your water pipes. If there are any water pipes IN the detached structure where the new panel is located, they must be bonded to the ground bar in the subpanel. If these pipes are metal in the ground before entering that structure, then you must ground them within 5' of entering the detached building. If these pipes are just in the yard somewhere or at the house, you don't bond this panel to them.
You didnt' say what size wires are feeding the detached building. The size of these wires determines the minimum size wire to use for ground rods and water pipes. If you use #6 to the ground rods, that will be compliant with whatever size you've run. If the grounding wire in your feeder is at least #8, you can probably only drive one rod at the detached building and say that the feeder EGC is also the bonding wire to a second electrode at the house (assuming you have at least one rod there).
__________________
Mark
Kent, WA
suemarkp
View Public Profile
Send a private message to suemarkp
Find all posts by suemarkp
#
3
IP: 64.160.53.6
July 8th, 2005, 06:39 AM
Unregistered
Posts: n/a
The water pipes...
Quote:
Originally Posted by
suemarkp
Since you ran 4 wires (two hots, a neutral, and a grounding wire), you do the following:
DO NOT install the green bonding screw to the neutral bar -- it must remain electrically isolated from the panel. Install the white wire in your feeder here.
Buy an accessory ground bar for your panel if it didn't come with one and screw it to the panel chassis. The green or bare grounding wire in your feeder goes to this bar.
Install at least one ground rod, and maybe two. You have to have these even if you have a metal water pipe ground. The ground electrode conductor also goes to the ground bar in the subpanel. You can just drill a hole in the wall (angling downward) and run the ground wire through it, or do it nicer by installing a 1/2" PVC LB fitting and a length of PVC conduit down to the dirt.
I'm confused with your water pipes. If there are any water pipes IN the detached structure where the new panel is located, they must be bonded to the ground bar in the subpanel. If these pipes are metal in the ground before entering that structure, then you must ground them within 5' of entering the detached building. If these pipes are just in the yard somewhere or at the house, you don't bond this panel to them.
You didnt' say what size wires are feeding the detached building. The size of these wires determines the minimum size wire to use for ground rods and water pipes. If you use #6 to the ground rods, that will be compliant with whatever size you've run. If the grounding wire in your feeder is at least #8, you can probably only drive one rod at the detached building and say that the feeder EGC is also the bonding wire to a second electrode at the house (assuming you have at least one rod there).
...will be those that are now within about 10' of the structure. This one will be tapped into and taken into the garage. I used #8 stranded THHN for all 4 wires so it sounds as if a single ground rod is acceptable and use #8 or better solid copper to join the panel to the rod and the rod to the water pipe?
Thanks, Mark!
Unregistered
#
4
IP: 24.64.223.204
July 11th, 2005, 10:06 AM
Pat!
Junior Member
Join Date: Jul 2005
Location: Vancouver Island
Posts: 6
The Bonding Screw?
I have run feeder cable [two balck, one white, and one bare copper ground] from a main 100amp house panel to a main 100amp panel in my garage. The information on the garage panel states that in some applications the bonding screw should be removed and in some cases it should remain. The electricity in the garage will be used for general tools only. eg. welder, lathe, drill press, lights, etc. In laymans terms [someone who does not even know what all the abrievations mean], could someone tell me the reason why the white [common wire] is sometimes grounded and why sometimes it is not.
Pat!
View Public Profile
Send a private message to Pat!
Find all posts by Pat!
#
5
IP: 130.76.32.15
July 11th, 2005, 03:33 PM
suemarkp
Super Moderator
Join Date: Dec 2003
Location: Kent, WA
Posts: 7,798
The white wire is always grounded once at the main service. Normally, you are prohibited from regrounding it again except for detached structures with no grounded conductive paths back to the main panel (e.g. via CATV wires, metal pipes, etc). The reason for this is the neutral carries current, and it therefore has some voltage drop. The longer the run and the higher the current, the worse the voltage drop is.
If you have a detached building with only a 3-wire feeder (no separate grounding wire but a regrounded neutral), there will be a small current flowing between the detached building ground rod and the house ground rod. The current will be proportional to the voltage drop. Yes, this drop is only a few volts, so the current is minimal. But this current can bother animals that feed from grounded metal troughs, have a large distance from their front to back feet, and can sometimes cause corrosion. If there is a metallic path between the buildings, you could burn up a phone or CATV wire because it is effectively paralleling the neutral. Its also not good for noise/interference reasons.
If the panels are in the same building and the neutral was regrounded, the grounding wires of different circuits could have voltages between them, and again this voltage would be the same as the voltage drop on the neutral in the subpanel feeder. This can cause sparks when two grounded items touch each other and current flows from that few volts of voltage difference. This won't shock you, but causes arcs and can degrade the grounding conductors because they have a better integrity when they don't carry current.
If you run a 4th grounding wire to the detached structure and float the neutral, that grounding wire normally never carries current so it has no voltage drop. This keeps the earth at the same potential at each building so no current is flowing through the earth. This is the better setup and should be done unless cost prohibitive.
__________________
Mark
Kent, WA
suemarkp
View Public Profile
Send a private message to suemarkp
Find all posts by suemarkp
#
6
IP: 64.242.197.254
July 13th, 2005, 11:38 AM
bobm
Senior Member
Join Date: Oct 2004
Posts: 213
Mark,
>If you have a detached building with only a 3-wire feeder (no separate grounding wire but a regrounded neutral), there will be a small current flowing between the detached building ground rod and the house ground rod. <
Is this still within code tp have a detached building serviced with 3-wire or do new installions all have to be 4-wire?
Bob
bobm
View Public Profile
Send a private message to bobm
Find all posts by bobm
#
7
IP: 130.76.32.145
July 13th, 2005, 11:49 AM
suemarkp
Super Moderator
Join Date: Dec 2003
Location: Kent, WA
Posts: 7,798
NEC still allows a 3 wire feed to a detached structure as long as there are no grounded conductive paths between the structurees. However, some local codes mandate 4 wire feeds in all cases once past the main disconnect (e.g. Washington State).
__________________
Mark
Kent, WA
suemarkp
View Public Profile
Send a private message to suemarkp
Find all posts by suemarkp
#
8
IP: 24.64.223.204
July 13th, 2005, 10:26 PM
Pat!
Junior Member
Join Date: Jul 2005
Location: Vancouver Island
Posts: 6
Fourth wire?
So is it safe to say that if a fourth wire [bare copper] is used to continue the grounding from the house panel to the panel in the detached building, that the white common wire should not be grounded. Also since the panel in the detached building is grounded directly from the main panel in the house, is a grounding rod for the second panel no longer necessary?
Pat!
View Public Profile
Send a private message to Pat!
Find all posts by Pat!
#
9
IP: 130.76.32.145
July 14th, 2005, 10:20 AM
suemarkp
Super Moderator
Join Date: Dec 2003
Location: Kent, WA
Posts: 7,798
If you run a 4th grounding wire, you will always be code compliant. In this case, you DO NOT connect the neutral to the panel chassis or grounding bar. Only the 4th grounding wire connects to the panel chassis and ground bar and ground electrode conductor.
Whether you run 3 or 4 wires, a detached structure supplied by a feeder still must be regrounded to a ground electrode system. The ground electrode system at the main panel won't be of too much use for a detached structure because it is too far away -- too much impedance in the wire run.
__________________
Mark
Kent, WA
suemarkp
View Public Profile
Send a private message to suemarkp
Find all posts by suemarkp
#
10
IP: 64.242.197.254
July 14th, 2005, 10:38 AM
bobm
Senior Member
Join Date: Oct 2004
Posts: 213
>too much impedance in the wire run.<
I did read somewhere, that if you run #8 for ground to the detached structure, you can get away with only one Ground Rod since the ground rods at the main pannel will count. Is that correct or is there some maximum distance restriction?
What is the best way to connect the ground wire at the subpannel? Can you use a terminal connection that is bolted to the pannel can?
Thanks Bob
Last edited by bobm : July 14th, 2005 at
10:46 AM
.
bobm
View Public Profile
Send a private message to bobm
Find all posts by bobm
Page 1 of 2
1
2
>
«
Previous Thread
|
Next Thread
»
Currently Active Users Viewing This Thread: 1
(0 members and 1 guests)
Thread Tools
Show Printable Version
Email this Page
Display Modes
Linear Mode
Switch to Hybrid Mode
Switch to Threaded Mode
Posting Rules
You
may not
post new threads
You
may not
post replies
You
may not
post attachments
You
may not
edit your posts
vB code
is
On
Smilies
are
On
[IMG]
code is
On
HTML code is
Off
Forum Jump
User Control Panel
Private Messages
Subscriptions
Who's Online
Search Forums
Forums Home
Building
Building Codes - Commercial
Building Codes - Residential
Electrical Code - CANADIAN
Electrical Code - USA
Plumbing Codes - Residential
Electrical Examinations & Brag Board Category
Brag Forum
Electrical Exam Preparations
Environment
Septic Systems
Water Quality
Horror Section
Construction Horror Stories
Wall of Shame
New Home, 'Planning a New Home'
New Homes - Building from the Ground Up
Outdoors, 'The Great Outdoors'
Camping
Firewood
Freshwater Fishing
Hunting & Tracking
Stories about The Great Outdoors
Yard & Garden
Repair
Appliance Repair
APPLIANCE POSTS / PLEASE READ....
Automotive
Boats
Building Construction - Existing Home
Computers & Data Wiring
Electrical - Existing Home
Electrical = Industrial / Commercial/Power Distribution
Energy Savings & Envelope Blanket of Structure - Existing Home
Heating & Air Conditioning - Existing Home
Home Security
Interference
Plumbing - Existing Home
Small Engines
Small Engines
Telephone Wiring
The Tool Shed
Suggestions & Help
Help on Using Our Site or Forums
Site Server Issues / Problems
Suggestions
Test Forum
Tips & Hints / Non - Interactive Forum Category
Appliances - Tips & Hints - NO QUESTIONS FOR HELP HERE
Electrical - Tips & Hints - NO QUESTIONS FOR HELP HERE
Plumbing - Tips & Hints - NO QUESTIONS FOR HELP HERE
Similar Threads
Thread
Thread Starter
Forum
Replies
Last Post
HELP... Pool Bonding Grid System for Above Ground Pool.
syburr
Electrical - Existing Home
14
May 27th, 2011
08:19 AM
Extending subpanel feeder's grounding conductor ?
mkepke
Electrical Code - USA
1
October 17th, 2005
04:48 PM
A topic very near and dear to our hearts--ground(s)
mudshvel
Electrical - Existing Home
4
September 2nd, 2003
07:56 PM
Other utilities co-bonding to ground electrode system
mudshvel
Electrical - Existing Home
2
June 7th, 2003
06:16 PM
Converting Non-grounded recepticle to a grounded recepticle
Anonymous
Building Construction - Existing Home
6
September 25th, 2002
10:08 PM
All times are GMT -4. The time now is
01:57 PM
.
Contact Us
-
Self Help and More
-
Archive
-
Top
Powered by vBulletin® Version 3.6.7
Copyright ©2000 - 2013, Jelsoft Enterprises Ltd.
© 2002 -
QuinStreet, Inc.
http://www.selfhelpforums.com