Default what exactly are "running threads that are prohibited by the code?

I understand running threads to be 2 pieces of rigid threaded pipe joined by a coupler. Is this correct? If not, what are running threads?

Is a 3 piece union required any place 2 threaded ends of pipe meet?

Specifically, I was looking at the scrap pile and saw 2 threaded ends of 2" rigid each 4 feet long. I pieced them together with a coupler and used it for a service riser. I was proud of the fact I saved $50 for a stick of Rigid 2", but was wondering if those were indeed running threads, as prohibited by code.

Thanks guys!

PS, it should be noted that rigid pipe SUCKS!
Reply With Quote
  #2   IP: 68.193.88.245
Old April 6th, 2005, 12:08 PM
Ron's Avatar
Ron Ron is offline
Senior Member
 
Join Date: Dec 2003
Location: New York
Posts: 293
Default

http://www.tpub.com/ceb/71.htm
__________________
Ron
Reply With Quote
  #3   IP: 66.59.122.169
Old April 6th, 2005, 04:34 PM
mdshunk's Avatar
mdshunk mdshunk is offline
Senior Member 'Self Help Guru'
 
Join Date: Jan 2004
Posts: 4,199
Default

Like Ron's great link shows...
Running threads are the cheaters way of getting out of using a 3 piece coupling (a.k.a. Erickson coupling). You'll see this from time to time. I've never (fingers crossed, looking up at the sky) done such a thing before.

There are, however, UL and inspector endorsed "running thread nipples", which are basically all-thread nipples that you can cut to length in the field. These get installed double locknutted. at both ends. You're not allowed to use a coupling with them.
__________________
"Nothing is foolproof to a sufficiently talented fool"
Reply With Quote
  #4   IP: 65.66.57.127
Old April 12th, 2005, 09:30 PM
paul paul is offline
Senior Member
 
Join Date: Apr 2004
Posts: 131
Default

So what then, would be an accepted use of a rigid coupling?
Reply With Quote
  #5   IP: 66.59.122.166
Old April 13th, 2005, 02:15 PM
mdshunk's Avatar
mdshunk mdshunk is offline
Senior Member 'Self Help Guru'
 
Join Date: Jan 2004
Posts: 4,199
Default

No, Paul. You don't get it. You can use a rigid coupling under almost any circumstance. "Running threads" are when you run 2 or three times the amount of required threads on one end of a piece of rigid so that you can spin the coupling completely on to one piece of the pipe, and then put another pipe up to the end of that one and spin the coupling onto the second piece, leaving it centered up. Some people "cheat" this way when you can't spin either piece of pipe. When you can't sping either piece of pipe to use a regular coupling, you need to use the 3 piece coupling or "erickson" coupling (sometimes improperly called a "union"). Under ordinary circumstances where you can spin at least one section of the rigid pipe, you can use the regular coupling.
__________________
"Nothing is foolproof to a sufficiently talented fool"
Reply With Quote
  #6   IP: 165.121.60.141
Old April 14th, 2005, 08:58 AM
Ohm1's Avatar
Ohm1 Ohm1 is offline
First Class Moderator

 
Join Date: Dec 2003
Location: WA
Posts: 4,631
Default

We call them all threads. Here is a pic of one that is listed:
__________________
Learning brings success. While you are waiting, I'm getting better!

Last edited by Ohm1 : September 28th, 2006 at 09:10 PM.
Reply With Quote
  #7   IP: 65.65.200.20
Old April 18th, 2005, 09:02 PM
paul paul is offline
Senior Member
 
Join Date: Apr 2004
Posts: 131
Default

Oh, I see said the blind man to his deaf daughter...

Thanks for the help!
Reply With Quote
Reply






Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Poor Building Codes magnets Building Codes - Residential 6 May 22nd, 2006 07:04 PM
New vs. old code changes Jacksnap Electrical Code - USA 4 September 2nd, 2004 05:43 PM
Code and more links may help Wgoodrich Electrical - Existing Home 1 June 15th, 2003 07:29 PM
Code and more links may help Wgoodrich Plumbing - Existing Home 0 May 21st, 2003 05:33 PM
Code and more links may help Wgoodrich Electrical = Industrial / Commercial/Power Distribution 0 May 21st, 2003 05:27 PM


All times are GMT -4. The time now is 07:57 AM.


Powered by vBulletin® Version 3.6.7
Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.
© 2002 - QuinStreet, Inc.
http://www.selfhelpforums.com