Default furnace starting but fan motor not running

Hello,
Im having some problems with my furnace. It is firing up and burning for about 5 mins and shutting down. the read out on the mother board is "thermal protection device open". I thought that because the furnace was heating up but the blower wasnt kicking on that maybe the furnace was overheating. So i pulled the motor and tried to find another with no success, but im really not sure that the motor is bad. I also checked to see if i was getting power to the motor and i read 124 volts to the motor. I would appreciate any input as I am rather a novice.
Reply With Quote
  #2   IP: 74.5.147.28
Old December 4th, 2010, 10:40 AM
Mr T's Avatar
Mr T Mr T is offline
Rotaredom

 
Join Date: Dec 2003
Location: LaLa Land, NW Ohio
Posts: 4,641
Default

Does the blower come on when you you turn the fan switch on the thermostat from auto to on?
Reply With Quote
  #3   IP: 65.185.116.226
Old December 4th, 2010, 03:51 PM
CCONRAD CCONRAD is offline
Junior Member
 
Join Date: Dec 2010
Posts: 2
Default

Mr T,
Thnaks for the reply. No it does not come on at all. I jump the two thermostat wires together. The furnace ignites and warms up and the exusust fan does run. After three mins or so the furnace then shuts down. and the red light flashes four times indicating "thermal protection device open". I removed the motor from the unit and wired it directly to an outlet and it started up and ran. The furnace is an Armstrong ultra sx95. Thanks for any type of direction.
Chad
Reply With Quote
  #4   IP: 74.5.147.28
Old December 4th, 2010, 11:20 PM
Mr T's Avatar
Mr T Mr T is offline
Rotaredom

 
Join Date: Dec 2003
Location: LaLa Land, NW Ohio
Posts: 4,641
Default

If you only have 2 wires going to your t stat then you wont be able to turn just the blower on.

Does the blower shut down at the same time as the burner?

There likely is no way for the unit to detect the thermal cutout in the blower, also a blower is self cooling so it overheating is not common.

More then likely it's a heat exchanger over temp (high limit switch) trip. This is often caused by lack of airflow through the heat exchanger.

A few things to check.....Make sure all your room registers are open, check the filter. Look for a forgotten about second filter (only need one). If the furnace was run without a filter, the AC evap or secondary heat exchanger (if you have either) could be plugged up and may need a professional cleaning. Also, if your blower requires oil every few years and the bearings went dry they could be damaged which can slow the unit down which will raise your heat exchanger temp. If you haven't oiled the bearings and they are due, add oil. (refer to your manual) If the blower is making noises when spun by hand or while it's spinning up/down then the bearings may be going.

If you look at the terminal strip where your t stat wires connect to the furnace (may be under a metal cover, disconnect AC power first), you may see a terminal marked G, or have a green wire on it.. that is your fan signal.. jump from red (should have a wire going to your t stat connected) to green then connect AC power.. the blower should run. If it runs and stays running then this will confirm your blower is good.
Reply With Quote
Reply






Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -4. The time now is 10:01 PM.


Powered by vBulletin® Version 3.6.7
Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.
© 2002 - QuinStreet, Inc.
http://www.selfhelpforums.com