Default Two GFCI Receptacles on 3-wire Circuit?

I'm armpit deep in a kitchen rennovation. I am planning to add a 20Amp-T-slot GFCI duplex receptacle on either side of the sink. I've run 12/3 to the first outlet, and 12/3 to the second outlet. I was planning feeding each GFCI from the different legs of the multiwire circuit.

Homer has posted in another thread:

"You can't protect both legs of a multiwire circuit with two GFCI receptacles.....however if you split the multiwire circuit into two circuits where the neutral is no longer shared, then you can protect those two circuits with one GFCI receptacle on each circuit. So, you can run one 3-wire multiwire circuit into the first box, and splice into two 12/2 or 14/2 cables so the neutral is no longer shared. These two circuits can then be protected by GFCI receptacles."

I'm having trouble to conceptualize how this is different from a shared neutral situation. Isn't it still a shared neutral?
__________________
"If you think education is expensive - try ignorance." (Bok's law)

Steve
  #2   IP: 67.9.37.29
Old November 3rd, 2004, 03:11 PM
Jacksnap's Avatar
Jacksnap Jacksnap is offline
Senior Member
 
Join Date: Jul 2004
Location: Largo, FL
Posts: 450
Default

Doing it Homer's way means you are not sharing the neutral downstream of either device. You are feeding each device with it's own neutral. You are splitting the neutral before each GFCI (by using 12/2 not 12/3 as you said).
  #3   IP: 24.150.115.93
Old November 3rd, 2004, 03:53 PM
Homer's Avatar
Homer Homer is offline
Senior Member with Distinction
 
Join Date: Dec 2003
Location: Springfield
Posts: 947
Send a message via AIM to Homer
Default

Here's an example setup that hopefully shows that the downstream neutrals are not shared.

Remember, everything is powered somehow from a shared neutral or multiwire circuit. There's only 3 wires entering your home from the POCO transformer.

Also, you could use a multiwire circuit to power alternate GFCI receptacles in a string. That is Blk & Wht, Red & Wht, Blk & Wht, etc. The thing to remember in this case is that you can't use the 'load' terminals of the GFCIs. You would need a GFCI in every location.

Homer
Attached Thumbnails
Click image for larger version

Name:	ExMultiwireRec.jpg
Views:	1998
Size:	48.1 KB
ID:	212  

Last edited by Homer : November 3rd, 2004 at 04:50 PM.
  #4   IP: 172.156.251.49
Old November 3rd, 2004, 04:52 PM
Mr Fixit eh's Avatar
Mr Fixit eh Mr Fixit eh is offline
Super Moderator

 
Join Date: Feb 2004
Location: Ontario, Canada
Posts: 476
Default

I guess I wasn't entirely thinking clearly at 3am or so when I pulled through the 12/3 from 1st GFCI receptacle to the 2nd. The second leg would be carried by 12/2 just fine.

Are you saying that if I pigtail the neutral to the first GFCI, I can keep the neutral going to the 2nd GFCI? Or are you saying that you must physically splice in a tiny length of 12/2 to join from the 3-wire feed to the first GFCI. There won't be any receptacles downstream of either receptacle.

Sleep deprivation is like alcohol...neither one mixes well with planning out multiwire circuits

Thanks for your help/patience.

PS. Excellent sketches Homer
__________________
"If you think education is expensive - try ignorance." (Bok's law)

Steve
  #5   IP: 165.121.59.144
Old November 3rd, 2004, 04:55 PM
Ohm1's Avatar
Ohm1 Ohm1 is offline
First Class Moderator

 
Join Date: Dec 2003
Location: WA
Posts: 4,631
Default

Great schematic Homer! The receptacles being placed in the schematic makes for a good understanding!
__________________
Learning brings success. While you are waiting, I'm getting better!
  #6   IP: 24.150.115.93
Old November 3rd, 2004, 05:32 PM
Homer's Avatar
Homer Homer is offline
Senior Member with Distinction
 
Join Date: Dec 2003
Location: Springfield
Posts: 947
Send a message via AIM to Homer
Default

Quote:
Are you saying that if I pigtail the neutral to the first GFCI, I can keep the neutral going to the 2nd GFCI?
Yes.

Quote:
Or are you saying that you must physically splice in a tiny length of 12/2 to join from the 3-wire feed to the first GFCI.
No, you may wire one of the HOT wires of the 3-wire supply directly to the LINE side of the first GFCI receptacle.

Here is a sketch of the alternate method that I mentioned also.

Homer
Attached Thumbnails
Click image for larger version

Name:	ExMultiwireRec3.jpg
Views:	1242
Size:	65.5 KB
ID:	214  

Last edited by Homer : November 3rd, 2004 at 07:00 PM.
  #7   IP: 172.141.153.197
Old November 3rd, 2004, 09:13 PM
Unregistered
 
Posts: n/a
Default

Ok, I can do this. Both diagrams make sense to me.

I'm still struggling with the idea of "shared neutral". Are we talking about a situation where the neutral goes to the line terminal on the first GFCI, then goes from the load terminal on the first GFCI to the line terminal on the second GFCI without pigtails? 'Cause that just wouldn't work, right.

I've got to get some sleep. Maybe tomorrow I will understand the "doesn't work" scenario.
  #8   IP: 172.141.153.197
Old November 3rd, 2004, 09:15 PM
Mr Fixit eh's Avatar
Mr Fixit eh Mr Fixit eh is offline
Super Moderator

 
Join Date: Feb 2004
Location: Ontario, Canada
Posts: 476
Default

Oops. The "unregistered" is me.
__________________
"If you think education is expensive - try ignorance." (Bok's law)

Steve
  #9   IP: 64.231.138.53
Old November 4th, 2004, 08:25 AM
Guido Guido is offline
Senior Member with Distinction
 
Join Date: Oct 2004
Location: Toronto
Posts: 507
Default

Homer if you have the time can you please post a diagram of the wiring method that will NOT work, such as where you said "You can't protect both legs of a multiwire circuit with two GFCI receptacles".
Thanks.
________

Last edited by jeff1 : February 1st, 2012 at 05:25 AM.
  #10   IP: 24.150.115.93
Old November 4th, 2004, 02:51 PM
Homer's Avatar
Homer Homer is offline
Senior Member with Distinction
 
Join Date: Dec 2003
Location: Springfield
Posts: 947
Send a message via AIM to Homer
Default

Quote:
Originally Posted by Guido
Homer if you have the time can you please post a diagram of the wiring method that will NOT work, such as where you said "You can't protect both legs of a multiwire circuit with two GFCI receptacles".
Thanks.
Here is the classic example of an attempt to protect a split receptacle on a multiwire circuit by using 2 GFCI receptacles instead of a 2-pole GFCI breaker.

Homer
Attached Thumbnails
Click image for larger version

Name:	NoGoodMultiwire.jpg
Views:	1071
Size:	60.3 KB
ID:	216  
Closed Thread






Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
Multi wire circuit question ejluhn720 Electrical - Existing Home 3 March 15th, 2007 12:14 AM
GFI trips when comnnected to dishwasher *Lou the handyman Electrical - Existing Home 0 December 12th, 2003 11:46 AM
Grounding method question and adding new circuits question *dfulmer Electrical - Existing Home 0 December 12th, 2003 11:26 AM
wiring GFCI to regular receptacles downstream Anonymous Electrical - Existing Home 5 June 14th, 2003 07:14 AM
dimming lights burnjob Electrical - Existing Home 7 October 8th, 2002 04:37 PM


All times are GMT -4. The time now is 05:56 AM.


Powered by vBulletin® Version 3.6.7
Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.
© 2002 - QuinStreet, Inc.
http://www.selfhelpforums.com