Default ceiling wires touching recessed can????

I'm installing non ic remodel recessed cans in my kitchen ceiling. There is no insulation, however I found a wire that will come in contact with the can when installed. Is this ok? Also, how close can I get to a copper water pipe, pvc drainie and a of ceiling joists from the cans? I'm worried about the heat created. Thanks inadvance. water pipe

Last edited by turfgrass : December 5th, 2009 at 06:10 PM.
Reply With Quote
  #2   IP: 70.195.232.241
Old December 6th, 2009, 07:53 AM
Wgoodrich's Avatar
Wgoodrich Wgoodrich is offline
Super Moderator

 
Join Date: Sep 2002
Posts: 7,451
Default

If I remember right in the manufacturer's installation instructions a minimum of 2" clearance is required for anything from that nonIC tank. Check manufacturer's installation instructions to confirm my memory.

Good Luck

Wg
Reply With Quote
  #3   IP: 71.197.173.35
Old December 6th, 2009, 09:47 AM
Fischer Fischer is offline
Senior Member with Distinction
 
Join Date: Apr 2007
Posts: 817
Default

Quote:
Originally Posted by turfgrass View Post
I'm installing non ic remodel recessed cans in my kitchen ceiling. There is no insulation, however I found a wire that will come in contact with the can when installed. Is this ok? Also, how close can I get to a copper water pipe, pvc drainie and a of ceiling joists from the cans? I'm worried about the heat created. Thanks inadvance. water pipe
If you have enough slack in the line, you could take some plumbers tape (Vinyl not metal) and suspend the wire away from the can, or pull it to the side maintaining 2" of separation. Copper plumbing lines shouldn't be a problem, but I'd reroute if I could. PVC would probably deform if too close and the main problem would be if it's directly above the can, and again, I would reroute. You could also place a sheet metal deflector between the can and anything else you might worry about. Take a strip of sheet metal long enough to span the floor/ceiling joists and screw it in between the object and can making sure nothing is touching. Also you have the choice of putting in a CFL or LED bulb, but then you don't know who is going to change the bulb in the future.
Reply With Quote
  #4   IP: 209.91.54.95
Old December 6th, 2009, 10:40 AM
Ohm1's Avatar
Ohm1 Ohm1 is offline
First Class Moderator

 
Join Date: Dec 2003
Location: WA
Posts: 4,631
Default

The separation is most likely 3 inches in all directions.

I would return the non-IC and install IC rated. Not a big difference in price.

With IC: Then install a short piece of insulation between the cable, and plumbing pipe. (Note: The only separation between the pipe and recess can will be the insulation)
__________________
Learning brings success. While you are waiting, I'm getting better!
Reply With Quote
  #5   IP: 71.233.49.113
Old December 6th, 2009, 05:25 PM
turfgrass turfgrass is offline
Senior Member
 
Join Date: Nov 2005
Posts: 396
Default

Are there 4" remodel ic rated cans? Also, the 3" clearance is just from the bulb house and not including the wire box??? If that box touches something would that be a problem?

Last edited by turfgrass : December 6th, 2009 at 05:27 PM.
Reply With Quote
  #6   IP: 71.174.88.209
Old December 6th, 2009, 05:27 PM
scuba_dave's Avatar
scuba_dave scuba_dave is offline
Senior Member 'Self Help Master with Distinction'
 
Join Date: Nov 2004
Location: Boston, MA
Posts: 1,511
Default

No way to move the wire just a little ?
The IC rated cans are MUCH bigger then the non-IC can
So if you can't move the wire an IC can will not fit
Even an inch away would do it

Will it touch the side...top...?
__________________
DIY Homeowner...not a Pro or licensed electrician
Reply With Quote
  #7   IP: 71.233.49.113
Old December 6th, 2009, 05:57 PM
turfgrass turfgrass is offline
Senior Member
 
Join Date: Nov 2005
Posts: 396
Default

There are can locations that I'm having trouble installing. The first spot, is an inch from the ceiling joist because a water line was in the way, forcing me to move closer to the joist. So, I guess I can install a sheet metal barrier against the joist. The wire box also gets close to a pvc drain line and a passing wire. Is the wiring box a fire hazard, or can object come in contact? Secondly, I removed a flourescent light strip above the sink and want to replace with a similar recessed can. The problem is there are several wires(3 way junction) that may touch the light housing when pushing the can up to install. Not sure what to do here. Thanks.
Reply With Quote
  #8   IP: 209.91.54.95
Old December 6th, 2009, 08:23 PM
Ohm1's Avatar
Ohm1 Ohm1 is offline
First Class Moderator

 
Join Date: Dec 2003
Location: WA
Posts: 4,631
Default

No they do not have 4" IC rated remodels.
__________________
Learning brings success. While you are waiting, I'm getting better!
Reply With Quote
  #9   IP: 71.197.173.35
Old December 6th, 2009, 09:06 PM
Fischer Fischer is offline
Senior Member with Distinction
 
Join Date: Apr 2007
Posts: 817
Default

Track lights.
Reply With Quote
  #10   IP: 66.31.118.114
Old December 7th, 2009, 06:40 AM
turfgrass turfgrass is offline
Senior Member
 
Join Date: Nov 2005
Posts: 396
Default

can either a copper, pvc pipe or a wire touch the electrical box that extends away from the housing?
Reply With Quote
Reply






Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -4. The time now is 05:39 AM.


Powered by vBulletin® Version 3.6.7
Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.
© 2002 - QuinStreet, Inc.
http://www.selfhelpforums.com