Default Maximum number of breakers in a switchboard

I have been told that if I have more than six breakers or disconnects in a switchboard that I need a main breaker. The switchboard is 575 volts, 2000 amp bus. A main breaker would increase my cost significantly. 230.71 mentions the max number of disconnects but it doesn't say I need a main breaker.

Can anyone offer me some help?
Reply With Quote
  #2   IP: 75.207.28.126
Old November 20th, 2009, 10:21 AM
Wgoodrich's Avatar
Wgoodrich Wgoodrich is offline
Super Moderator

 
Join Date: Sep 2002
Posts: 7,451
Default

The answer to the question word for word as you asked it is yes and no. Reason for this is conditions you did not mention. If this panel is a main service rated panel in a main structure with no previous overcurrent device aka breaker or fuse then the 6 disconnect rule applies. Each breaker in that panel would be considered as a mian service rated disconnect with 6 being the maximum you can have. The above statement for example would be a panel fed directly from a service company meterbase and not prior fuse or breaker. A second example of this being a yes answer would be if you are feeding a detached accessory structure from a main structure. The fuse or breaker installed in that accessory detached structure where the feeder entered would have a maximum of 6 disconnect rules including the number of breakers in a main lug only panel without a main breaker.

If the question you asked is concerning a panel that is a slave from a main service rated panel in the same building as that main service rated panel the answer would be no a main would not be required and the 6 disconnect rule would not apply. This is because there is a fuse or breaker in the same building that can be used as the main form of disconnect and this panel being a slave of the main panel would be a subpanel thus not being a main service rated panel. If your panel is a slave of a main service rated panel being a sub panel of that main panel then there would be no limit.

Even though breakers in a panel are circuit breakers if there is no other means of shutting off that panel then the 6 disconnect rule would apply. Sub panels have a breaker in a panel feeding power to that subpanel that will shut of that entire subpanel then the 6 disconnect rule does not apply.

They often call the 6 disconnect rule in other words maximum of 6 sweeps of the hand to shut down power coming from that panel.

Hope this helps

Wg
Reply With Quote
  #3   IP: 209.91.54.95
Old November 20th, 2009, 10:35 AM
Ohm1's Avatar
Ohm1 Ohm1 is offline
First Class Moderator

 
Join Date: Dec 2003
Location: WA
Posts: 4,631
Default

Quote:
Originally Posted by Paul Kluesner View Post
I have been told that if I have more than six breakers or disconnects in a switchboard that I need a main breaker. The switchboard is 575 volts, 2000 amp bus. A main breaker would increase my cost significantly. 230.71 mentions the max number of disconnects but it doesn't say I need a main breaker.

Can anyone offer me some help?


Need more information.

To add:
For services, If we look at 230.71(A), you will find that it presents that no more than 6 handles shall disconnect a service from the structure being served.

Yet, for a detached building--being fed from another. You should look at Part 2 of NEC 225 . (Special attention to 225.36)
__________________
Learning brings success. While you are waiting, I'm getting better!
Reply With Quote
  #4   IP: 65.203.178.1
Old November 23rd, 2009, 06:36 AM
Paul Kluesner Paul Kluesner is offline
Junior Member
 
Join Date: Nov 2009
Posts: 2
Default Thanks

Thanks for the replies. This switchboard is being fed by five generator strings, the 6th breaker is for a capacitor bank. I hope this is enough information.
Reply With Quote
  #5   IP: 75.205.55.133
Old November 24th, 2009, 02:03 PM
Wgoodrich's Avatar
Wgoodrich Wgoodrich is offline
Super Moderator

 
Join Date: Sep 2002
Posts: 7,451
Default

Now you caused much more confusion and lack of info needed. What do you mean by 5 generator leads. Are you saying you have hooked five generators to five different breakers to feed this panel ? What is the capacitor connection used for ?

Wg
Reply With Quote
  #6   IP: 72.38.178.108
Old November 24th, 2009, 02:16 PM
joed's Avatar
joed joed is offline
Super Moderator

 
Join Date: Dec 2003
Location: Welland Ontario
Posts: 4,690
Default

This sounds way beyond DIY which this site is for. Sounds like you have 6 generators powering a site with a capacitor bank for power factor correction.
Reply With Quote
  #7   IP: 96.50.79.109
Old November 24th, 2009, 06:52 PM
moto moto is offline
Senior Member
 
Join Date: Nov 2008
Location: Victoria, BC, Canada
Posts: 120
Default

It was way beyond DIY when he mentioned 575 volts and 2000 amps....
Reply With Quote
  #8   IP: 71.174.88.209
Old November 25th, 2009, 05:50 AM
scuba_dave's Avatar
scuba_dave scuba_dave is offline
Senior Member 'Self Help Master with Distinction'
 
Join Date: Nov 2004
Location: Boston, MA
Posts: 1,511
Default

What I can't have 2,000a residential service ?

I have a big Christmas display !!
__________________
DIY Homeowner...not a Pro or licensed electrician

Last edited by scuba_dave : November 25th, 2009 at 08:20 AM.
Reply With Quote
  #9   IP: 209.91.54.95
Old November 25th, 2009, 08:04 AM
Ohm1's Avatar
Ohm1 Ohm1 is offline
First Class Moderator

 
Join Date: Dec 2003
Location: WA
Posts: 4,631
Default

I agree, if the OP is not a Licensed Electrician (Contractor). Yet, if the OP an electrical professional, then we are here to help.
__________________
Learning brings success. While you are waiting, I'm getting better!
Reply With Quote
  #10   IP: 64.83.217.86
Old November 25th, 2009, 04:30 PM
junkcollector junkcollector is offline
Senior Member 'Self Help Master'
 
Join Date: Jun 2007
Location: Central Minnesota
Posts: 1,421
Default

I thought this site was for professionals and DIY'ers alike. Heck we even have a Commercial / industrial section.
Reply With Quote
Reply






Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -4. The time now is 07:55 PM.


Powered by vBulletin® Version 3.6.7
Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.
© 2002 - QuinStreet, Inc.
http://www.selfhelpforums.com