Default Size of Wire for Central Air Conditioner 4ton and 3 ton.

What wire should I use?

Thanks Brent
Reply With Quote
  #2   IP: 68.193.85.189
Old August 20th, 2004, 11:37 AM
Ron's Avatar
Ron Ron is offline
Senior Member
 
Join Date: Dec 2003
Location: New York
Posts: 293
Default

Tell us the information from the nameplate of the units. They will typically indicate minimum circuit ampacity, in addition to other rinformation.
__________________
Ron
Reply With Quote
  #3   IP: 24.161.81.158
Old August 20th, 2004, 12:55 PM
Speedy Petey's Avatar
Speedy Petey Speedy Petey is offline
Senior Member with Distinction
 
Join Date: Dec 2003
Location: NY State
Posts: 906
Default

Also if you are talking about the condensor alone or both air handler and condensor. They do need separate circuits.
Reply With Quote
  #4   IP: 128.221.4.201
Old August 24th, 2004, 05:50 AM
Collins Collins is offline
Junior Member
 
Join Date: Jul 2004
Posts: 13
Default

2500 watts on the 2 1/2 ton and 4500 watts on 4 ton. So I'm thinking that I need a 30amp and a 50 amp circuit. Wire should be 10/3 for 30 amp and 6/3 for the 50 amp. I'm I thinking correctly?
Reply With Quote
  #5   IP: 130.76.32.15
Old August 24th, 2004, 12:21 PM
suemarkp suemarkp is offline
Super Moderator

 
Join Date: Dec 2003
Location: Kent, WA
Posts: 8,265
Default

Watts is not the ideal value we need. If that is all you have, we need volts too (I'm assuming 240V). Is there anything that says Mimimum Circuit Ampacity (or MCA), Rated Load Amps (RLA), Full Load Amps (FLA), and/or Maximum Fuse/Breaker? The value we need is MCA, but if that isn't there then we need the motor FLA and the compressor RLA.

From the few AC compressors I've looked at recently, a 2.5 Ton 240V unit would have an MCA of 18 to 23 amps which requires a #10 copper branch circuit (#12 is OK if MCA is less than 20). The breaker installed on this wire would probably be a 25 or 30A depending on what the manufacturer says. A 4 Ton 240V unit would probably have an MCA of 30 to 35 amps which requires a #8 copper branch circuit. The breaker for this would need to be a 40 or 50A breaker again depending on what the manufacturer allows.

You can upsize the wire to the customary sizes for the breaker if you wish -- will be a more efficient installation that way but cost a little more.
__________________
Mark
Kent, WA
Reply With Quote
  #6   IP: 114.59.192.242
Old May 31st, 2010, 09:59 AM
centralairunits centralairunits is offline
Junior Member
 
Join Date: May 2010
Posts: 3
Default

I have the similar case,

Thank's a lot for the complete answer particularly on " You can upsize the wire to the customary sizes for the breaker if you wish -- will be a more efficient installation that way but cost a little more."
__________________
no spam here

Last edited by centralairunits : May 31st, 2010 at 10:07 AM.
Reply With Quote
  #7   IP: 24.41.32.240
Old May 31st, 2010, 01:52 PM
Ohm1's Avatar
Ohm1 Ohm1 is offline
First Class Moderator

 
Join Date: Dec 2003
Location: WA
Posts: 4,631
Default

This thread is almost 6 years old.
__________________
Learning brings success. While you are waiting, I'm getting better!
Reply With Quote
Reply






Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -4. The time now is 01:57 AM.


Powered by vBulletin® Version 3.6.7
Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.
© 2002 - QuinStreet, Inc.
http://www.selfhelpforums.com