Default Amps per leg in 3 phase

So this falls into the category of "it should be obvious" but its actually got us completely confused

Our datacenter offers us "208 3 phase 60 amp" service. We will hook that to a trio of 208 single phase power distribution units, each attached to one pair of phase leads. The PDUs have only ammeters to tell us how much current they are drawing. How many amps can each PDU draw before the feed is overloaded?

I've heard answers ranging from 15-60 amps.

One method I was given was based on watts. 208 x 1.73 x 60 = 21590w. Divided by 3 legs = 7196watts per PDU. Divide that by 208V per PDU = 34.6 amps.

Ideas?
Thanks
Reply With Quote
  #2   IP: 207.35.6.2
Old December 17th, 2007, 11:19 AM
joed's Avatar
joed joed is offline
Super Moderator

 
Join Date: Dec 2003
Location: Welland Ontario
Posts: 4,591
Default

The simplest answer is usually the correct one. I would say 60 amps per unit.
Reply With Quote
  #3   IP: 207.114.255.2
Old December 17th, 2007, 01:06 PM
mfarver mfarver is offline
Junior Member
 
Join Date: Mar 2005
Posts: 25
Default

I confirmed that the 3 phase breaker for the supply is in fact rated 60 amps, if that affects the answer.

Mark
Reply With Quote
  #4   IP: 24.150.120.191
Old December 17th, 2007, 05:12 PM
Homer's Avatar
Homer Homer is offline
Senior Member with Distinction
 
Join Date: Dec 2003
Location: Springfield
Posts: 947
Send a message via AIM to Homer
Default

A 60A 3-phase branch circuit has 60A available on each leg. So you have 60A available on each leg for your loads. Here is a breakdown of your situation of the delta connected single phase loads.

So in summary, when each single phase 208V load is drawing 34.64A, the 3-phase line current will be 60A.

However, since these units should be considered to be a continuous load (3 hours or longer), then a 60A branch circuit should only be loaded to 80% of 60A. This takes you down even further, to 0.8x 34.68 = 28A.

To complete this discussion consider the following scenario as well (not what you have). If you had three Wye connected single phase loads, then they could each draw 60A while the 3-phase line current remained at 60A. However, the voltage across your Wye connected loads would only be 120V. The power would be the same (root3 x 60 x 208 ) or (3 x 60 x 120) for this 60A branch circuit.

Homer
Attached Thumbnails
Click image for larger version

Name:	Image4.jpg
Views:	77
Size:	67.3 KB
ID:	1830  
__________________
Depending on your skills, doing your own electrical work may risk the health and safety of the community. Always find out how to do things safely before beginning.

Last edited by Homer : December 17th, 2007 at 06:06 PM.
Reply With Quote
  #5   IP: 67.171.2.84
Old December 17th, 2007, 09:19 PM
suemarkp suemarkp is offline
Super Moderator

 
Join Date: Dec 2003
Location: Kent, WA
Posts: 8,190
Default

Homer's got the right answer. Because of the confusion that can happen in 3-phase, especially if you mix 120V with 208V loads, it is best to work in watts. The continuous load makes things worse. Your only saving grace will be the power draw of the servers. They rarely draw thier nameplate rating (and dual power supplies don't double the power draw either).

The ammeters will help you know your actual draw, so limit each PDU to 28 amps.
__________________
Mark
Kent, WA
Reply With Quote
  #6   IP: 207.114.255.2
Old December 19th, 2007, 06:50 PM
mfarver mfarver is offline
Junior Member
 
Join Date: Mar 2005
Posts: 25
Default

Thanks for the clear and excellent description! (It turns out, my math was right... sometimes even I get lucky)

Mark
Reply With Quote
Reply






Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -4. The time now is 05:07 AM.


Powered by vBulletin® Version 3.6.7
Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.
© 2002 - QuinStreet, Inc.
http://www.selfhelpforums.com