Default Wiring GFCI with Black, White and Red

Good evening: I have replaced all receptacles in teh past 3 homes I owned. Recently bought a home built in 1968. I attempted to replace the kitchen receptacles with GFCIs. However, when I pulled the existing receptaclres from their boxes, each contains 2 black, 2 white and 2 red wires. I assume the red are hot like the black, but what are they and how do I wire the line and load of the GFCI?

Thank you for your time.
Reply With Quote
  #2   IP: 24.22.213.59
Old October 9th, 2007, 09:47 PM
suemarkp suemarkp is offline
Super Moderator

 
Join Date: Dec 2003
Location: Kent, WA
Posts: 8,261
Default

You most likely can't do it with GFCI receptacle. This is most likely a "multiwire branch circuit" which is basically two separate circuits that share a common neutral. These may have been wired "canadian style" where the red is powering say the top receptacle and the black does the lower one.

The only way you can GFCI this is to use a double pole GFCI breaker. Unfortunately, these cost well over $100 each if you can even find one for your panel.

The only solution I can offer is to abandon either the red or black and put a GFCI first on the outlet run. Then, at some point along the counter outlet run, don't daisy chain anymore and run a new circuit to the remaining receptacles. If running a new wire to any of the receptacles is not feasible (you can cut the new feed in at any receptacle), you're stuck with a DP GFCI breaker solution.
__________________
Mark
Kent, WA
Reply With Quote
  #3   IP: 75.11.36.143
Old October 9th, 2007, 11:43 PM
Roger's Avatar
Roger Roger is offline
Senior Member 'Self Help Master with Distinction'
 
Join Date: Aug 2004
Location: Kansas
Posts: 1,645
Default

If you put in gfci's I believe things will work provided you put a gfci at each location and only pigtail the neutral and hot to the line of the gfci...no load connections. Alternate with black to the gfci at one location then pass the red thru and then connect red to the next gfci and so on.

Kind of expensive though.

Last edited by Roger : October 10th, 2007 at 05:53 AM.
Reply With Quote
  #4   IP: 24.22.213.59
Old October 10th, 2007, 07:50 AM
suemarkp suemarkp is offline
Super Moderator

 
Join Date: Dec 2003
Location: Kent, WA
Posts: 8,261
Default

Great solution -- totally forgot about not using the load side of the GFCI! Your solution is still probably cheaper than a double pole GFCI unless he has over 10 receptacles to do.
__________________
Mark
Kent, WA
Reply With Quote
  #5   IP: 207.35.6.2
Old October 10th, 2007, 08:56 AM
joed's Avatar
joed joed is offline
Super Moderator

 
Join Date: Dec 2003
Location: Welland Ontario
Posts: 4,646
Default

Are you in Canada? It used to be code to require split wired receptacles in the kitchen. It is not a requirement to upgrade these to GFCI. If you do you must change them to 20 amp circuits. The current code requires either split 15 amp or unsplit 20 amp on kitchen counters.
Reply With Quote
  #6   IP: 4.233.173.166
Old October 10th, 2007, 10:18 AM
AllanJ AllanJ is offline
Senior Member with Distinction
 
Join Date: Jan 2006
Posts: 916
Default

With just three outlet boxes you might get away with non-split circuitry, one GFCI serving just the first box using red and pigtailed white, and one other GFCI in the second box using only black and white and also serving the third box if any via its load terminals. Subject to having 12 gauge wires if non-split circuitry at and beyond the first box needs 20 amps.

Since you mentioned the kitchen I might add that it is not good to have the refrigerator on a GFCI protected circuit. Using individual receptacle GFCI's can solve this dilemma.

Last edited by AllanJ : October 11th, 2007 at 06:41 AM.
Reply With Quote
Reply






Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments