Replacing meter base abd moving main breaker panel
I am replacing an old fused panel that is on the outside of the house with a 200 amp breaker main, and putting in a new meter base. I will be using 4/0 SER.
The new panel will be about 50 ft from the meter into a utility room and will run through the attic space, do I need to put this in conduit? If so what size.
Also the utility co wants a 200 amp meter base with a safety disconnect, any recommendations for brand and model # would be appreciated.
Thanks
044runner
044runner
View Public Profile
Send a private message to 044runner
Find all posts by 044runner
#
2
IP: 98.247.156.18
November 1st, 2009, 09:59 PM
suemarkp
Super Moderator
Join Date: Dec 2003
Location: Kent, WA
Posts: 5,088
This is usually not allowed. Under the NEC, and most other codes, there is a very limited distance inside the building that service conductors may go before hitting the main disconnect device. The disconnect must contain a fuse or breaker, and not just a lever in the meter can. In most areas, you can go 3 to 15 feet inside the house before hitting this disconnect.
But you also said SER. SER is 4 conductors, and is used after the main disconnect. SEU is 3 conductors and is used between the meter and the main disconnect. SO perhaps you need to clarify further what you're trying to do. Is it meter only (no main breaker in the meter enclosure) then 50' to the main disconnect? If so, the SEU for this must remain outside for most of that distance. If you put a fused disconnect right next to the meter and then run SER through the attic, then there is no distance limitation.
As to whether that needs conduit is another local interpretation. SE cables must be protected from physical damage. What is subject to damage and how you mitigate it are typically local inspector calls. Running it in sch 80 PVC, EMT, or rigid metal conduit will certainly work, but you should use individual THWN wires instead of SER cable in that case -- easier to pull, cheaper, and the conduit can be smaller.
__________________
Mark
Kent, WA
suemarkp
View Public Profile
Send a private message to suemarkp
Find all posts by suemarkp
#
3
IP: 64.83.217.86
November 2nd, 2009, 12:19 PM
junkcollector
Senior Member 'Self Help Master'
Join Date: Jun 2007
Location: Central Minnesota
Posts: 1,186
Sounds to me like he's gonna use a meter main and then use SER to hit is panel (subpanel) inside.
junkcollector
View Public Profile
Send a private message to junkcollector
Find all posts by junkcollector
#
4
IP: 209.91.54.95
November 2nd, 2009, 04:59 PM
Ohm1
Super Moderator
Join Date: Dec 2003
Location: Washington State
Posts: 3,577
Quote:
Also the utility co wants a 200 amp meter base with a safety disconnect, any recommendations for brand and model # would be appreciated.
If the POCO wants you to use a specific type of Meter, then call them, they will have a list.
__________________
Learning brings success
Ohm1
View Public Profile
Send a private message to Ohm1
Find all posts by Ohm1
#
5
IP: 216.155.212.135
November 4th, 2009, 03:56 AM
044runner
Junior Member
Join Date: Oct 2009
Posts: 3
Thanks for your help, I will be using a meter main, then on to the utility room to the panel with SER (unless there is a better alternative to SER.)
Thanks again Paula
044runner
View Public Profile
Send a private message to 044runner
Find all posts by 044runner
#
6
IP: 70.194.188.39
November 4th, 2009, 08:43 AM
Wgoodrich
Super Moderator
Join Date: Sep 2002
Posts: 7,115
I suspect we are having some communication gaps. If what you are calling a meter main is a meter with a main breaker in it that will shut off the whole house then this will be your main service rated panel built into the meter or having a meter then a weatherproof fused disconnect next to the meter. This set up would make the panel inside a subpanel controlled by the main service disconnect outside requiring the SER four wire cable you spoke of.
If you are passing through the attic not being nearest point of entrance, the above discription is required having a main service rated disconnect outside making that panel inside to be a slave of that main outside disconnect.
You would use a 3 wire SEU type cable only if there is no main fused or breaker or disconnect.
Hope this helps
Wg
Wgoodrich
View Public Profile
Send a private message to Wgoodrich
Find all posts by Wgoodrich
#
7
IP: 216.155.212.135
November 5th, 2009, 04:22 AM
044runner
Junior Member
Join Date: Oct 2009
Posts: 3
OK, lets see if I get it right this time....
Meter main with a disconnect, (or weatherproof fused disconnect next to meter>>>> SER thru the attic to subpanel in the utility room
Thanks again for your help!
044runner
View Public Profile
Send a private message to 044runner
Find all posts by 044runner
#
8
IP: 75.206.186.211
November 5th, 2009, 06:24 PM
Wgoodrich
Super Moderator
Join Date: Sep 2002
Posts: 7,115
Yes, a breaker or fused disconnect next to the meter makes your panel inside a nonservice rated panel aka sub panel thus requiring 3 wires found in an SER cable.
Good Luck
Wg
Wgoodrich
View Public Profile
Send a private message to Wgoodrich
Find all posts by Wgoodrich
«
Previous Thread
|
Next Thread
»
Currently Active Users Viewing This Thread: 1
(0 members and 1 guests)
Thread Tools
Show Printable Version
Email this Page
Display Modes
Linear Mode
Switch to Hybrid Mode
Switch to Threaded Mode
Posting Rules
You
may not
post new threads
You
may not
post replies
You
may not
post attachments
You
may not
edit your posts
vB code
is
On
Smilies
are
On
[IMG]
code is
On
HTML code is
Off
Forum Jump
User Control Panel
Private Messages
Subscriptions
Who's Online
Search Forums
Forums Home
Building
Building Codes - Commercial
Building Codes - Residential
Electrical Code - CANADIAN
Electrical Code - USA
Plumbing Codes - Residential
Electrical Examinations & Brag Board Category
Brag Forum
Electrical Exam Preparations
Environment
Septic Systems
Water Quality
Horror Section
Construction Horror Stories
Wall of Shame
New Home, 'Planning a New Home'
New Homes - Building from the Ground Up
Outdoors, 'The Great Outdoors'
Camping
Firewood
Freshwater Fishing
Hunting & Tracking
Stories about The Great Outdoors
Yard & Garden
Repair
Appliance Repair
APPLIANCE AID SITE
Automotive
Boats
Building Construction - Existing Home
Computers & Data Wiring
Electrical - Existing Home
Electrical = Industrial / Commercial/Power Distribution
Energy Savings & Envelope Blanket of Structure - Existing Home
Heating & Air Conditioning - Existing Home
Home Security
Interference
Plumbing - Existing Home
Small Engines
Small Engines
Telephone Wiring
The Tool Shed
Suggestions & Help
Help on Using Our Site or Forums
Site Server Issues / Problems
Suggestions
Test Forum
Tips & Hints / Non - Interactive Forum Category
Appliances - Tips & Hints - NO QUESTIONS FOR HELP HERE
Electrical - Tips & Hints - NO QUESTIONS FOR HELP HERE
Plumbing - Tips & Hints - NO QUESTIONS FOR HELP HERE
All times are GMT -4. The time now is
04:13 AM
.
Contact Us
-
Self Help and More
-
Archive
-
Top
Powered by vBulletin® Version 3.6.7
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
(c) 2008 Self Help and More 'All Rights Reserved'
http://www.selfhelpforums.com