Proper kitchen receptacle wiring
My kitchen has 3 above-counter split receptacles. Each is wired with a double 15A breaker (for a total of 6 individual circuits, taking up 6 slots in the panel). There is nothing else on these breakers.
Is this the required method by the CEC (Ontario), or can I daisy-chain two receptacles (while maintaining the top/bottom split).
If this is allowed it would free up 2 much needed spaces in the panel.
________
Buy Cannabis Seeds
Last edited by Guido : February 25th, 2011 at
04:23 AM
.
Guido
View Public Profile
Send a private message to Guido
Find all posts by Guido
#
2
IP: 24.150.115.93
October 20th, 2004, 02:46 PM
Homer
Senior Member with Distinction
Join Date: Dec 2003
Location: Springfield
Posts: 947
Quote:
Originally Posted by
Guido
My kitchen has 3 above-counter split receptacles. Each is wired with a double 15A breaker (for a total of 6 individual circuits, taking up 6 slots in the panel). There is nothing else on these breakers.
Is this the required method by the CEC (Ontario), or can I daisy-chain two receptacles (while maintaining the top/bottom split).
Yes, you can have a maximum of two 15A split receptacles on each double pole 15A breaker.
They must be arranged so that the split receptacles on the same breakers are not adjacent to one another. If you do combine them, do not double lug your breakers. You need to connect them in a box outside of your panel. Under Canadian rules you can't make any splices inside the panel. The only exception is for panel replacement and existing wires are too short to terminate in the new panel.
Just keep in mind that under current code, you need to protect these with those
expensive
double pole GFCI breakers. Because this is a
multiwire or shared neutral
setup, you
can't
use two GFCI receptacles to protect the two legs.
Just to mention, there is now an alternate strategy permited. You can use 20A receptacles on 20A circuits and protect them with the 20A T-slot GFCI receptacles. However, this doesn't do you any good since you have 14/3 cable already installed and not #12.
Homer
Last edited by Homer : October 20th, 2004 at
06:40 PM
.
Homer
View Public Profile
Send a private message to Homer
Find all posts by Homer
#
3
IP: 64.231.228.243
October 21st, 2004, 06:08 AM
Guido
Senior Member with Distinction
Join Date: Oct 2004
Location: Toronto
Posts: 502
Quote:
Originally Posted by
Homer
If you do combine them, do not double lug your breakers.
Is this a "kitchen only" rule? Because I know some of my breakers currently have 2 wires under the screw (but I was told that type of breaker was designed for 2 wires so it's OK).
Quote:
Originally Posted by
Homer
Just keep in mind that under current code, you need to protect these with those
expensive
double pole GFCI breakers. Because this is a
multiwire or shared neutral
setup, you
can't
use two GFCI receptacles to protect the two legs.
Sorry, I'm confused. Please bear with me.
How is the above setup different than what you mentioned in the other thread:
"So, you can run one 3-wire multiwire circuit (12/3 or 14/3) into the first box, and splice into two 12/2 or 14/2 cables so the neutral in no longer shared. These two circuits can then be protected by GFCI receptacles."
I don't understand why one is considered shared neutral, and the other isn't (they both seem the same to me).
Quote:
Originally Posted by
Homer
Just to mention, there is now an alternate strategy permited. You can use 20A receptacles on 20A circuits and protect them with the 20A T-slot GFCI receptacles. However, this doesn't do you any good since you have 14/3 cable already installed and not #12.
Homer
That would be my last case option. The kitcken is located above the panel, so it's not out of the question, but it's still a lot of work, and a lot of money (20A double pole breaker is $50 alone!).
________
VOLCANO DIGITAL
Last edited by Guido : February 25th, 2011 at
04:23 AM
.
Guido
View Public Profile
Send a private message to Guido
Find all posts by Guido
#
4
IP: 24.150.115.93
October 21st, 2004, 02:18 PM
Homer
Senior Member with Distinction
Join Date: Dec 2003
Location: Springfield
Posts: 947
Quote:
Is this a "kitchen only" rule? Because I know some of my breakers currently have 2 wires under the screw (but I was told that type of breaker was designed for 2 wires so it's OK).
This has nothing to do with the location of the circuit. There are a few breakers that are approved for two wires. Make sure that yours are.
Quote:
Sorry, I'm confused. Please bear with me.
How is the above setup different than what you mentioned in the other thread:
"So, you can run one 3-wire multiwire circuit (12/3 or 14/3) into the first box, and splice into two 12/2 or 14/2 cables so the neutral in no longer shared. These two circuits can then be protected by GFCI receptacles."
I don't understand why one is considered shared neutral, and the other isn't (they both seem the same to me).
They
are
both shared neutral multiwire circuits.
Until recently, the code specifically stated that the kitchen counter receptacles had to be
split receptacles
. Split receptacles are fed from multiwire circuits. You cannot protect a split receptacle with anything other than a 2-pole GFCI breaker because the neutral is shared right at the receptacle.
If you replaced the 15A split receptacles with 15A non-split receptacles you would be in violation of the code.
Recently, because of this problem, the code was changed to allow you to choose between;
1) Two 15A multiwire circuits with split receptacles and a 2-pole GFCI breaker.
and
2) Two 20A circuits protected by 20A T-slot GFCI receptacles.
So, you have the split receptacles on multiwire circuits based on the older code before GFCI protection was required. Protecting the existing split receptacles can only be done with an expensive 2-pole GFCI breaker.
Homer
Homer
View Public Profile
Send a private message to Homer
Find all posts by Homer
#
5
IP: 64.231.228.243
October 22nd, 2004, 05:18 AM
Guido
Senior Member with Distinction
Join Date: Oct 2004
Location: Toronto
Posts: 502
Just curious - when did the code change allowing non-split 20A receptacles in the kitchen?
Thank you very much for all your help, bit by bit it's all coming together. I appreciate it.
I just saw the electrical forum - did I post this in the wrong place? If so I'll ask the moderator to move it. I was looking for Canadian specific content.
________
VAPORIZER VOLCANO
Last edited by Guido : February 25th, 2011 at
04:24 AM
.
Guido
View Public Profile
Send a private message to Guido
Find all posts by Guido
#
6
IP: 24.150.115.93
October 22nd, 2004, 02:42 PM
Homer
Senior Member with Distinction
Join Date: Dec 2003
Location: Springfield
Posts: 947
This is the right place for Canadian specific questions.
In January 2003, Ontario made amendments to these sections of the 2002 CEC.
Here is a
link
to a bulletin.
Homer
Last edited by Homer : October 22nd, 2004 at
02:51 PM
.
Homer
View Public Profile
Send a private message to Homer
Find all posts by Homer
#
7
IP: 148.78.243.122
October 24th, 2004, 12:34 PM
Wgoodrich
Super Moderator
Join Date: Sep 2002
Posts: 7,451
Homer good catch on the ammendment. However I noticed this ammendment only applies to Ontario not other provinces. Did you catch that part of only one provice involved?
Wg
Wgoodrich
View Public Profile
Send a private message to Wgoodrich
Find all posts by Wgoodrich
#
8
IP: 24.150.115.93
October 24th, 2004, 12:53 PM
Homer
Senior Member with Distinction
Join Date: Dec 2003
Location: Springfield
Posts: 947
Quote:
Originally Posted by
Wgoodrich
Did you catch that part of only one province involved?
Yes, Ontario is the jurisdiction of the poster. His profile shows his home to be Toronto.
I do not know if any other provinces have made similar ammendments but we can't make that assumption.
Any forum readers in other provinces should abide by the original split-receptacle requirements of the 2002 CEC.
Homer
Homer
View Public Profile
Send a private message to Homer
Find all posts by Homer
#
9
IP: 64.231.228.243
October 25th, 2004, 09:27 AM
Guido
Senior Member with Distinction
Join Date: Oct 2004
Location: Toronto
Posts: 502
Yup, I'm in Toronto. Thanks!
I just read that notice and the wording seems like GFCI protection is required only for receptacles WITHIN ONE METER of sinks. I always thought it was for EVERY kitchen counter receptacle.
If I'm not mistaken, the US allows 15A receptacles on a 20A circuit IF there is more than 1 receptacle on that circuit. Am I correct? If so, what is the reasoning behind allowing lower rated receptacles than the circuit can provide? Isn't this an obvious hazard?
________
FREE XXX MOVIES
Last edited by Guido : February 25th, 2011 at
04:25 AM
.
Guido
View Public Profile
Send a private message to Guido
Find all posts by Guido
#
10
IP: 130.76.32.144
October 25th, 2004, 12:10 PM
suemarkp
Super Moderator
Join Date: Dec 2003
Location: Kent, WA
Posts: 7,822
Something with a 15A plug should not be drawing more than 15 amps. Therefore, a 20A breaker shouldn't be a hazard. The hazard is avoided when you have a single receptacle, but given a duplex receptacle, you can utilize the full 20A when using both receptacles (say 15A + 5A).
If a short circuit occurs, both 15A and 20A breakers trip at the same level of short circuit current. All 15A UL listed receptacles should be rated for 20A passthrough with 15A going to any one set of prongs, since this is specifically permitted in the NEC.
If canadian code never allowed 15A receptacles on 20A circuits, then the listing agencies may never have tested them for 20A passthrough and they could be a hazard. Hopefully, everything you have is both CSA and UL listed.
__________________
Mark
Kent, WA
suemarkp
View Public Profile
Send a private message to suemarkp
Find all posts by suemarkp
Page 1 of 2
1
2
>
«
Previous Thread
|
Next Thread
»
Currently Active Users Viewing This Thread: 1
(0 members and 1 guests)
Thread Tools
Show Printable Version
Email this Page
Display Modes
Linear Mode
Switch to Hybrid Mode
Switch to Threaded Mode
Posting Rules
You
may not
post new threads
You
may not
post replies
You
may not
post attachments
You
may not
edit your posts
vB code
is
On
Smilies
are
On
[IMG]
code is
On
HTML code is
Off
Forum Jump
User Control Panel
Private Messages
Subscriptions
Who's Online
Search Forums
Forums Home
Building
Building Codes - Commercial
Building Codes - Residential
Electrical Code - CANADIAN
Electrical Code - USA
Plumbing Codes - Residential
Electrical Examinations & Brag Board Category
Brag Forum
Electrical Exam Preparations
Environment
Septic Systems
Water Quality
Horror Section
Construction Horror Stories
Wall of Shame
New Home, 'Planning a New Home'
New Homes - Building from the Ground Up
Outdoors, 'The Great Outdoors'
Camping
Firewood
Freshwater Fishing
Hunting & Tracking
Stories about The Great Outdoors
Yard & Garden
Repair
Appliance Repair
APPLIANCE POSTS / PLEASE READ....
Automotive
Boats
Building Construction - Existing Home
Computers & Data Wiring
Electrical - Existing Home
Electrical = Industrial / Commercial/Power Distribution
Energy Savings & Envelope Blanket of Structure - Existing Home
Heating & Air Conditioning - Existing Home
Home Security
Interference
Plumbing - Existing Home
Small Engines
Small Engines
Telephone Wiring
The Tool Shed
Suggestions & Help
Help on Using Our Site or Forums
Site Server Issues / Problems
Suggestions
Test Forum
Tips & Hints / Non - Interactive Forum Category
Appliances - Tips & Hints - NO QUESTIONS FOR HELP HERE
Electrical - Tips & Hints - NO QUESTIONS FOR HELP HERE
Plumbing - Tips & Hints - NO QUESTIONS FOR HELP HERE
Similar Threads
Thread
Thread Starter
Forum
Replies
Last Post
changed outlet
ifustigateyou
Electrical - Existing Home
6
October 30th, 2006
02:20 AM
wiring a new receptacle from an existing one
*vanguard8624
Electrical - Existing Home
1
December 14th, 2003
10:32 PM
K & T replacement how much $$
Anonymous
Building Construction - Existing Home
3
January 18th, 2003
01:16 PM
Question from email transferred to forum by Wg
Wgoodrich
Electrical - Existing Home
1
November 1st, 2002
03:52 PM
Kitchen-Garage Electrical Layout
SharpT
Electrical - Existing Home
13
October 5th, 2002
12:05 AM
All times are GMT -4. The time now is
10:32 AM
.
Contact Us
-
Self Help and More
-
Archive
-
Top
Powered by vBulletin® Version 3.6.7
Copyright ©2000 - 2013, Jelsoft Enterprises Ltd.
© 2002 -
QuinStreet, Inc.
http://www.selfhelpforums.com