  1. Default Air Compressor trips Breaker

    Any Ideas?

    I borrowed my dad's air compressor and when I plug it in the garage it will try to start and trip the breaker (20A breaker and it seems fine as I can run an number of other things on it without tripping). It sputs and sputters to try to get going, until it trips the breaker. However if I bleed the air off in the tank, it will start up fine and run until it hits the high pressure shut off.

    I am thinking that the starting capacitor on the motor is getting weak and this is showing when starting against the pressure in the tank. I would think that the "run" capacitor is fine as it runs fine once it starts. I think I will stop by Grainger's to see if they have a new starter capacitor on the way home.

    What are other's thoughts. Am I chasing the wrong thing?

  2. #2


    While it could be the start cap, I'd rather suspect the more common check valve or unloader valve.
    "Nothing is foolproof to a sufficiently talented fool"

  3. #3
    Join Date
    Jan 2005
    east of MrT, west of MDShunk, north of Jacksnap, south of Mr Fixit, eh


    also check the nipple from tank to pres. sw./unloader. moisture causes them to rust/clog up.
    some mornings i wake up grouchy...............others i let her sleep

  4. Default

    Quick update.

    I changed the starting Cap. and the thing still spits and sputters and finally trips the breaker. (now I think it is because it is starting against a Load) '

    Next step is to tear the check valve out and see if I can see any problems. I tripped the unloader valve (on the side of the pressure switch) with my finger and it seems to let the pressure off.

    Thanks for the suggestions.


  5. #5
    homebild Guest

    Default Distance to Outlet

    How far from the outlet do you have the compressor plugged in?

    If it's on an extension cord over 50 feet long you can get these symptoms.

  6. Default

    It's just the 5-6 foot cord on the compressor itself plugged directly into the outlet (and I tried several outlets).

    Thanks for the suggestion though.


  7. #7
    Join Date
    Dec 2004
    columbus grove ohio

    Default aircompressor sputter

    your problem is the unloader valve if the compressor will start and run with no pressure in the tank. starting under load draws high current that will kick the breaker. when unloaded, the flywheel gets up to speed quickly and keeps everything rolling. i'm guessing your running current is very close to your breaker size.

  8. #8


    See this link: http://www.epinions.com/content_160758861444

    The bottom line is this: Craftsman compressors are known for
    bad capacitor centrifugal switches, which trip C/B's.

  9. Default Situation Update

    OK the compressor is still tripping the 20 A breaker (actually it will trip any of several breakers - so it is not just a weak breaker)

    I cleaned the air intake filters and still had the problem.
    I tried changing the starting Capacitor and still had the problem.
    I have checked the operation of the unloader and check valves and they seem to be working fine.
    I changed the oil in the Compressor pump crankcase to a synthetic oil and I still have the problem.

    A little bit more info on the compressor. It is a PUMA brand compressor (model PK-3022, 3 HP, 21 gallon tank, 9.3 cfm) that was bought in 1992. It has a 2 cylinder belt driven compressor pump. The motor has both a Start Capacitor and a Run Capacitor. (like I said I tried changing the start capacitor with no luck). The symptoms seem somewhat temperature related - that is it shows up when the compressor is cold (haven't had any "warm" temperatures in North Idaho the past several months to see if it goes away when it is warm) . Once I get it started (ususally by bleeding all the air in the tank) and it runs enough to get "warmed-up", the compressor will run fine (switching on when the pressure in the tank drops and shutting off at the upper limit), unless it sets for too long with out running and then it will trip the breaker again.

    The problem seems to be related to the switching between the "Start Mode" and the "Run Mode" on the motor. The motor starts and trys to switch modes and then it ends up switching back to the start mode. This goes on until it ends up tripping the breaker. While it is doing this "coughing" of trying to get up to speed I can see some arcing if I get down and look in the vents of the motor. "ggratec" posted to a link for a similar sort of problem for a direct drive craftsman compressor. I think I will try to have a look at the motor and see if it has a similar problem.

    Like I said the thing seems to run fine once it gets "warmed-up". If it didn't run so good when it was warmed-up I would think about changing the motor that drives the belt.

    Any other ideas or suggestions.


  10. #10


    I don't claim to be a compressor expert (mechanical end of it),
    however, it still sounds like you need to replace/repair the
    capacitor switch. Sounds like the switch is stuck in the "run"

Thread Information

Users Browsing this Thread

There are currently 2 users browsing this thread. (0 members and 2 guests)

Similar Threads

  1. Should one pole on main breaker be warm?
    By Unregistered in forum Electrical - Existing Home
    Replies: 7
    Last Post: December 16th, 2004, 09:57 PM
  2. Breaker design
    By *Olathe in forum Electrical - Existing Home
    Replies: 1
    Last Post: December 14th, 2003, 02:03 PM
  3. can't find replacement breaker
    By otter712 in forum Electrical - Existing Home
    Replies: 1
    Last Post: September 26th, 2003, 10:04 AM
  4. GE Wall Oven swapped for Kenmore - Wiring to in-line breaker
    By Anonymous in forum Appliance Repair
    Replies: 3
    Last Post: February 14th, 2003, 04:28 PM
  5. Installing Sauna Upgrade 15 AMP Breaker to 20 AMP Breaker
    By Anonymous in forum Electrical - Existing Home
    Replies: 1
    Last Post: January 3rd, 2003, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts