Thread: 15 amp outlets and 20 AMp breaker

  1. #1

    Default 15 amp outlets and 20 AMp breaker

    Is this allowable. I am finishing my basement. I have a few packages of standard home 15 amp outlets, I am wondering if a 15 amp outlets are allowable to hook to a 20 amp circuit braker in the service panel. I plan on doing nothing more than plugging in veryday equipt to these. TV stereo etc. No shop tools, pumps, motors...etc. just plain ol outlets. I have a book that states that the outlets should be apropriate for the amperage of the circuit but doesn't specify what that means. The wiring is a 12/2 gauge. My upstairs was done by professional contractors and they hooked 15 amp outlets to 20 amp breakers but I still need to know. Thanks.

  2. #2
    Join Date
    Jan 2003
    Location
    welland ontario
    Posts
    372

    Default

    Yes it is permissable to use 15 amp outlets on a 20 amp circuit.

  3. #3

    Default

    Only time you can't do that is if a single receptacle is on the circuit.

    You're fine if you're using duplex receptacles.
    Scott Sabin

  4. #4

    Default

    Quote Originally Posted by ssabin
    Only time you can't do that is if a single receptacle is on the circuit.
    Does this mean that if a single receptacle is anywhere on the circuit, the rest of the receptacles must have a matching amp rating?

  5. #5

    Default

    I suspect you may have misunderstood what ssabin meant to say. A dedicated branch circuit with a single hole receptacle must be rated equal to the amp rating of that dedicated branch circuit.

    If you have a branch circuit with multiple single hole receptacles in that branch circuit then you have a branch circuit where you could install 15 or 20 amp single receptacles in that 20 amp rated multioutlet branch circuit.

    SSabin was referring to a dedicated circuit with a single outlet serving a dedicated load, not a multioutlet branch circuit. At least this is what I think he meant to say.

    Also it is a Code violation to install 20 amp receptacle or receptacles whether single or duplex on a 15 amp 14 awg branch circuit.



    Hope this helps

    Wg

  6. #6

    Default

    Should have thought of "single" and "singleplex" meaning different things.

    Let's see if I have this right .

    If the circuit is dedicated (has only one outlet), the amps must match, period.

    On a 20 amp circuit with multiple receptacles, I can mix and match 15 and 20 amp outlets, either singleplex or duplex, to my heart's content.

    On a 15 amp circuit with multiple receptacles, I can use any combination of singleplex and duplex receptacles as long as they're designed for a 15 amp circuit.

    How am I doing?

  7. #7

    Default

    NEC 2002

    210.21.B
    (B) Receptacles.
    (1) Single Receptacle on an Individual Branch Circuit. A single receptacle installed on an individual branch circuit shall have an ampere rating not less than that of the branch circuit.

    (3) Receptacle Ratings. Where connected to a branch circuit supplying two or more receptacles or outlets, receptacle ratings shall conform to the values listed in Table 210.21(B)(3),


    The table say not to exceed 15 amp receptacles on a multioutlet branch circuit rated for 15 amps maximum wire or breaker size.

    15 or 20 amp receptacles allowed on a multioutlet branch circuit rated for 20 amp maximum wire or breaker size.

    The NEC does not care if single plug receptacle or duplex receptacle. The NEC only cares that a dedicated circuit with only one load or outlet must be a receptacle rated in amps equal to teh amp rating of that dedicated branch circuit serving only one utilization equipment.

    Hope this helps

    Wg

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. Breaker Panel Questions
    By QueenBee in forum Electrical Code - USA
    Replies: 10
    Last Post: December 6th, 2006, 06:11 PM
  2. Power at breaker but none at outlets
    By Jesse in forum Electrical - Existing Home
    Replies: 8
    Last Post: November 12th, 2006, 05:28 PM
  3. Partial Wall Outlets Not working on Same Breaker
    By Unregistered in forum Electrical - Existing Home
    Replies: 7
    Last Post: June 16th, 2005, 09:46 PM
  4. How many outlets and switches to each breaker?
    By Unregistered in forum Electrical Code - USA
    Replies: 11
    Last Post: May 1st, 2005, 10:44 AM
  5. Bad Circuit Breaker?
    By *Guest in forum Electrical - Existing Home
    Replies: 0
    Last Post: December 12th, 2003, 02:34 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •