    What is considered a room with Information Technology Equipment. Is a 10'x10' room with a couple of servers and PC's considered a Information Technology Equipment Room requiring EPO's, dedicated HVAC and fire rated partitions.
    If you think it is an IT Room, then what about an office space with a couple of PC's, why would it be different.

    Official definitions would be helpful.

  2. #2
    Join Date
    Sep 2002


    Posted by: Wgoodrich
    Posted: Tue Sep 10, 2002 9:58 pm

    The following is a copied section of the rule in the NEC 2002;

    645.2 Special Requirements for Information Technology Equipment Room.


    Notice the above copied section of the rule in 645.2 in capital letters. This states that all 5 conditions listed in sections of the rule 645 that must exist before NEC 645 rule applies;

    Also read the following NEC 2002 HANDBOOK COMMENTARY; See if this helps for confirmation;

    The requirements in Article 645 are based on the assumption that the room complies with NFPA 75, Standard for the Protection of Electronic Computer/Data Processing Equipment.
    The requirements in Article 645 amend the first four chapters of the Code. This article has less stringent requirements for electrical installations in rooms that comply with NFPA 75, provided that the five prerequisites in 645.2 are satisfied.
    Article 645 applies only to equipment and wiring located within the information technology equipment room. An information technology equipment room is an enclosed area, with one or more means of entry, that contains computer-based business and industrial equipment. It is designed to comply with the special construction and fire protection provisions of NFPA 75, as well as 645.2 of the Code.
    Small terminals, such as remote telephone terminal units, remote data terminals, personal computers, and cash registers in stores and supermarkets, are not covered by Article 645.

    The last sentence in the rule 645.2 and the last sentence in the commentary in the NEC handbook should settle your thoughts.

    Let us know if this helps


  3. #3
    Join Date
    Sep 2002


    Posted by: HandyRon
    Posted: Wed Sep 11, 2002 9:38 am

    Wow. It is amazing what I miss, when hopping and skipping through various sentances in code articles. I thought for sure I had 645.2 nailed as code requirements, but you have pointed out the word "provided", which of course, now rereading, makes the entire article optional (unless we have decided to implement NFPA 75). They were conditions to the article and not requirements to follow as part of the article.

    Excellent point. Thanks

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. HELP... Pool Bonding Grid System for Above Ground Pool.
    By syburr in forum Electrical - Existing Home
    Replies: 14
    Last Post: May 27th, 2011, 12:19 PM
  2. Electrical Q's How do they Measure Kilowatts
    By JimR in forum Electrical = Industrial / Commercial/Power Distribution
    Replies: 14
    Last Post: July 9th, 2005, 12:04 PM
  3. When is NEC/AHJ not needed?
    By imported_marako in forum Electrical - Existing Home
    Replies: 4
    Last Post: July 2nd, 2003, 09:11 PM
  4. ARTICLE 645 Information Technology Equipment
    By imported_Ron in forum Electrical - Existing Home
    Replies: 4
    Last Post: January 17th, 2003, 12:17 AM
  5. Converting Non-grounded recepticle to a grounded recepticle
    By Anonymous in forum Building Construction - Existing Home
    Replies: 6
    Last Post: September 26th, 2002, 02:08 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts