    HI, I have a 2.5 ton Ruud central unit (upstairs) which will not respond in any way to the thermostat: neither fan nor compressor-condensing unit will run or do anything. Unit is about 5 years old.
    I have a Fluke meter and have accomplished some pretty serious auto repairs, but haven't much experience with central AC units. If someone could offer suggestions where to start looking, I might be able to find the problem.
    I have checked the breakers and the outdoor disconnect for the condensing unit already.
    Thanks

  2. #2
    Join Date
    Dec 2003
    Location
    LaLa Land, NW Ohio
    Posts
    4,762

    Default

    Check the breakers for the indoor unit. THere may be a in site disconnect/fuse/switch near the indoor unit too. Check for any status LED's in your unit. If all checks out ok. Check doors for safety switches (especialy around your blower). Then check for voltage (about 24V) to your thermostat/coming from the transformer.

  3. #3

    Default Ruud AC

    HI; OK I will check the thermostat for 24v and get back to you.
    When I removed the front door of the air-handling unit, I saw a circuit board; I hate those things; it's probably bad and costs $$$.
    Anyway, more later, and thanks!

  4. #4
    Join Date
    Dec 2003
    Location
    LaLa Land, NW Ohio
    Posts
    4,762

    Default

    Did you check your indoor breakers too? there will be 2 sets of breakers for your unit...indoor+outdoor. THe voltage at your thermostat will be AC voltage. Forgot to mention that earlier.

  5. #5

    Default Ruud AC

    Hi; OK, I have 24 VAC at the thermostat (the thermostat is a simple thing with a mercury switch, not a complex electronic, programmable (although I am planning to get 2 of those).
    My unit has 2, 220VAC breakers in the electrical panel: one for the condensor unit (outdoor unit) and one for the blower (indoor) unit. Additionally, there is a disconnect at the outdoor unit: pull out the handle, and it is disconnected.
    Next step?

  6. #6
    Join Date
    Dec 2003
    Location
    LaLa Land, NW Ohio
    Posts
    4,762

    Default

    Pull out your manual and see if your unit utilizes error codes.
    If not, pull out your manual and see if there is a schematic. Trace out your fan relay see if anything is getting to it.

  7. #7

    Default Ruud A/C won't

    OK. this afternoon I verified: the outdoor (compressor-condenser unit) will run perfectly if I engage the starter plunger manually. I cleaned the dust and bugs out of it while I had the cover off. Saw the nice Copeland scroll compressor; everything else looked OK.
    I tried jumpering the red-yellow and red-green control wires at the thermostat; nothing.
    I checked the red-yello again for 24v, and, no voltage (with the Fluke meter in the correct range this time).
    OK, the thermostat control circuit has lost its power supply; I assume it is located in the front of the blower cabinet; I will check it out tonight, after the attic cools off.
    Update later, Randy
    Last edited by RandyR; August 7th, 2005 at 03:59 PM.

  8. #8

    Default Problem Solved

    Turns out there is a little switch, float operated, on the edge of the overflow pan the indoor unit sits in; this switch is supposed ot turn the unit off if the pan fills with water (condensate) before it ruins the ceiling. This switch was poorly installed, had come loose and was sitting there, tripped; hence, no A/C.
    Simple problem; did not cost anything to get the unit going (Phew!), and I learned some things about my units.

    Thanks Mr. T for the assistance. Remember: I am only an amateur. If you have a problem with a gas-turbine engine or piston engine of 2000-12000 horsepower, or a gas compressor, just let me know; those I know.

  9. #9
    Join Date
    Dec 2003
    Location
    LaLa Land, NW Ohio
    Posts
    4,762

    Default

    Glad to hear it's fixed

    Sorry, my engine is 13000 HP... but thanks anyways!

  10. #10

    Default RUUD central A/C compressor and Fan won't come on

    Hello,

    I have somewhat of a similar problem. I have a RUUD 2 ton A/C unit (upstairs). The compressor nor the fan will come on, so no a/c upstairs. When the thermostat is turned on to cool, the compressor will make a humming noise approximately every 30 - 45 secs, like it's trying to kick on. In my troubleshooting I have replaced the "contactor" and the "delay on timer switch" to no avail. I'm not an a/c person so I'm at the end of my limited expertise. I'm wondering now is there anything else that can be done? Is there any hope? My system specs are as follows: A/C Unit info: Model - UAKA-024JAZ, Volts - 208-230, Compressor: R.I.A. 12.2/12.2, HP watts 1/6. Compressor: copeland, model: ZR23K1-PVF-230, oil: 26oz .77L, LRA block 62.5. I hope that I provided enough info, and thanks in advance for any help you can provide.

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. Double Pole Thermostat Dilemma
    By Tony D in forum Electrical - Existing Home
    Replies: 1
    Last Post: October 19th, 2006, 05:58 PM
  2. Thermostat for use with Heat Pump
    By skipatroller in forum Energy Savings & Envelope Blanket of Structure - Existing Home
    Replies: 2
    Last Post: October 16th, 2006, 07:52 PM
  3. Programmable Thermostat for Heat Pump?
    By skipatroller in forum Heating & Air Conditioning - Existing Home
    Replies: 0
    Last Post: October 11th, 2006, 03:48 PM
  4. adding 24v thermostat
    By rustyherman in forum Heating & Air Conditioning - Existing Home
    Replies: 2
    Last Post: January 26th, 2006, 09:01 PM
  5. Replacing an electric baseboard thermostat
    By *Mike in forum Heating & Air Conditioning - Existing Home
    Replies: 0
    Last Post: December 12th, 2003, 12:21 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •