Thread: Recommended Generator Hookup

  1. #1

    Default Recommended Generator Hookup

    I live in a mobile home with 200amp service. I have a Portable generator which puts out 6500 continuous watts with 53 amps.

    Just checking to make sure I need a 200amp transfer switch and inlet box capable of 55amps.

    I plan on mounting the inlet box approx no more than 25 feet from the power panel in the mobile home.

    Any specific recomendations would be helpful...

  2. #2
    Join Date
    Dec 2003
    Location
    Kent, WA
    Posts
    8,431

    Default

    Most generators are 120/240V, so it is really putting out 26.5A on each leg. So a 30A 120/240V (4 wire) inlet would be sufficient. There are many ways to install this. But if you're putting it in that 200A feeder, it needs to be rated for 200A. Gives you the most options, as all of your breakers could be run from the generator. You'll have to watch your load, as you only have 26 amps per leg to work with -- won't be able to run a whole lot at once.
    Mark
    Kent, WA