Thread: wire size for air conditioner

  1. #1

    Default wire size for air conditioner

    I want to replace the wiring to a disconnect for an A/C Compressor.

    The plate on the compressor

    Unit Supply voltage: 208/230 - 1 - 60
    Minumun Circuit Ampacity: 25.2
    Maximum Fuse or HACR Breaker: 40

    1. What size wire should I use
    2. Does the Disconnect need to be fusible and if so is 40 amps too much
    3. What size breaker.

    right now a portion of the wire is 10/2 and the breaker is a 30 amp.
    I believe 10/2 is probably on the low side, can you please advice - thanks

  2. #2

    Default

    Since it says the minimum circuit ampacity is 25.2, you need a cable that will handle at least 25.2 amps. For this, #10 gauge is what you need so you're in fine shape there.

    Since it says that the maximum fuse or breaker size is 40 amps, then you may install either a 30 or 40 amp breaker. Normally, you'd only use a 30 amp breaker max for #10 gauge wire. Air conditioning equipment is one of the special exceptions in the code. Since you already have a 30 amp breaker installed, the a/c may run just fine. If you get some "nuisance tripping" of that 30 amp breaker, I would install a 40 amp breaker in the panel for sure trouble-free operation. OR... you can just swap out the 30 amp breaker for a 40 amp breaker right away. Your choice... no special hazard either way.

    No, the disconnect does not need to be fused. You may use a fused disconnect if you want to, but this would be redundant, since the overcurrent protection will be provided by the breaker in the panel. You can just use an ordinary weatherproof (nonfused) disconnect. These are really cheap (compared with the fused variety) and come in 30, 60, and 100 amp sizes. You may use a 30 amp size, but the 60 amp size is often more readily available and will be fine. Just a little more heavy duty.
    "Nothing is foolproof to a sufficiently talented fool"

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. Differences in "Old" & "New"14/2 WG Wire Size?
    By aggiehobbie in forum Electrical Code - USA
    Replies: 8
    Last Post: December 30th, 2010, 03:56 PM
  2. What size wire
    By gnarly in forum Electrical Code - CANADIAN
    Replies: 7
    Last Post: May 2nd, 2009, 01:27 AM
  3. 150' run to pool pump from house, what size wire?
    By fg4432 in forum Electrical Code - USA
    Replies: 1
    Last Post: March 30th, 2006, 05:52 PM
  4. Question about wiring a 50A welder
    By *Schwack in forum Electrical - Existing Home
    Replies: 0
    Last Post: December 12th, 2003, 03:15 PM
  5. Wire size for running 220ft to pollbarn?
    By sparkslarry in forum Electrical - Existing Home
    Replies: 3
    Last Post: July 25th, 2003, 11:32 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •