Thread: Gas meter clearance

  1. #1

    Default Gas meter clearance

    Where in the NEC does it state that a meterbase must be at least 5' from a natural gas meter ?

    Wg

  2. #2
    Join Date
    Dec 2003
    Location
    Kent, WA
    Posts
    8,427

    Default

    It doesn't. You may find it in your local power company requirements manual though. Perhaps its a NESC requirement, or maybe just a desirement.
    Mark
    Kent, WA

  3. #3
    Join Date
    Dec 2003
    Location
    WA
    Posts
    4,631

    Default

    The gas company may have a distance requirement---I know some State Electrical inspectors here are enforcing the distance requirements per gas utility requirements in some areas.
    Learning brings success. While you are waiting, I'm getting better!

  4. #4
    Join Date
    Dec 2003
    Location
    WA
    Posts
    4,631

    Default

    If it's a single utility company that serves the house or building, then they are definitely enforcing their own code. I can say with certainty that it's 3-5 feet between a gas meter vent and an above ground transformer. Then it's 5 feet between the edge of an LP gas tank, and a meter base. Yeah, it depends on the serving utility.

    This is directly from one of our serving utility companies:
    Minimum clearances from structures, building openings, and gas meters
    A minimum clearance of 3 feet is required between electric service lines and
    windows, doors, porches, fire escapes, or similar openings.
    A minimum horizontal clearance of 3 feet is required between electric service
    equipment and natural gas meter pressure relief vent
    (see Figure 14).
    Service lines passing over the roof of another structure (but not attached to that
    structure) must maintain the minimum clearances (see Figure 14).
    Service lines passing over a deck must maintain a minimum clearance of 11 feet
    (see Figure 14).
    Last edited by Ohm1; July 21st, 2009 at 07:39 PM. Reason: added LP tank and util example
    Learning brings success. While you are waiting, I'm getting better!

  5. #5

    Default

    Reason I asked is because it is hard to prove it is not in the Code. To my knowledge it was not in the NEC. However this 6' clearance idea has popped up now and then for decades. If anyone has a International Gas Fuel Code I would appreciate it if they would look to see if such a rule is in that code. To my knowledge of that code I remember it being there but only if the gas meter has a vent on the meter. I received a call from a past student that was hit with this rule today on the job site. The power company called to clarify why the gas meter was within 6' of a new commercial building electrical meter. Problem is the electrician installed the meterbase and had it inspected waiting for the power company to connect. By the time the power company came to connect they found the gas meter installed by the gas company after the electrical meter was installed to be within 6' of the electrical meter. I get those type calls to confirm if there is or is not a code. Hard to open a codebook and say see that rule is not there.

    Frustrating

    Wg

  6. #6
    Join Date
    Dec 2003
    Location
    Kent, WA
    Posts
    8,427

    Default

    I searched the 2008 code book (preliminary edition, so its not 100%) for "gas" and didn't see anything relevant. It was annoying in the chapters dealing with gas spacer cable and hazardous locations (flammable gases) because there we so many hits.
    Mark
    Kent, WA