Thread: service entrance and grounding

  1. #1
    Unregistered Guest

    Default service entrance and grounding

    I am placing a new service entrance and a new 200 amp service panel. The grounding requirements, I understand, is two 8 ft grounding rods 6 feet apart (since I have no water pipe within 5 feet of the entrance). My question. Do I connect the two grounding rods together with a # 6 continous wire or should each grounding wire have its own #6 wire and both run into the service entrance and bonded to the 200 amp panel? thanks

  2. #2


    You run one continous length of #6 copper from the ground bar in the panel and catch both ground rods. The wire will pass through the acorn clamp on the first rod without being broken.

    As for the water pipe, you may be confused. If the water pipe entering your home is metal of any sort, you have to run a #4 copper ground wire to it. The grounding connection must be made within the first five feet of the pipe where it enters the house. Your post sounded like you thought you only had to ground the water pipe if it was within five feet of the service entrance. This is not the case at all. If the pipe enters as metallic, you have to catch it with a ground wire within the first five feet.

  3. #3
    Unregistered Guest


    Thanks, that clears up a lot of confusion about the water pipe issue.

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. Generator install at main service disconnect
    By suemarkp in forum Electrical - Existing Home
    Replies: 52
    Last Post: February 7th, 2006, 01:37 PM
  2. service entrance load center grounding
    By Unregistered in forum Electrical Code - USA
    Replies: 2
    Last Post: July 16th, 2004, 06:51 PM
  3. New Service
    By *JOHNNY in forum Electrical - Existing Home
    Replies: 0
    Last Post: December 12th, 2003, 03:36 PM
  4. A topic very near and dear to our hearts--ground(s)
    By mudshvel in forum Electrical - Existing Home
    Replies: 4
    Last Post: September 2nd, 2003, 11:56 PM
  5. Other utilities co-bonding to ground electrode system
    By mudshvel in forum Electrical - Existing Home
    Replies: 2
    Last Post: June 7th, 2003, 10:16 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts