I have 3 phase 100 amp service that is delta wired (high leg configuration). Out of the meter I have 3 hot wires and a neutral coming out to a 3 phase 100 amp fuse box. From the fuse box I have 3 legs and a neutral running up into a breaker panel that is totally occupied (it only has space for 12 breakers). Running to the left of the fuse box are only 2 hots and a neutral (so there is no 3 phase in the second breaker panel). The above two breaker panels are get their power directly from the fuse box right after the meter, the lug nuts each have two 1 awg wires, except the high leg lug nut that only has one wire running into the upper breaker panel.
I need to install the following:
Table-Saw: 23.4 amp @ 220V 3 phase
Hinge Boring: 6 amps @ 220V 3 phase
Edge Bander: 16 amps @ 220V 3 phase
Line Borer (Future): 16 amps @ 220V 3 phase
Air Compressor: 15 amps @ 220V 1 phase
2 Dust Collectors: 6 amps @ 220V 1 phase X 2 = 12 amps @ 220V
I am figuring that the amps are in the place can do, since the machines will not all be on at the same time, and the existing breaker panels are mostly lights and office outlets.
Questions:
1) What is the difference between a load center and a breaker panel and where would you use each?
2) Can I eliminate the breaker panel to the left of the fuse box and add another 1 awg wire to the high leg lug nut, by replacing it with a bigger breaker panel? Each machinery will be on a dedicated circuit?
3) Can I use a 200 amps breaker panel instead of 100 amps so that if in the future I need to upgrade service, I won't have to do any rewiring?
4) I want to use 10 awg wire (12 awg will do, except for the table saw) and 20 amp breakers for all machines (30 amps breaker for table saw), is this safe?
5) I want to wire the machines with a quick disconnect plug, using SJ wire. Where do I connect the SJ wire ground? Do I connect in to the machine, the junction box, and how is the plug wiring connected? The SJ is running from the junction box to the machine with a quick connect. I am using metal conduit to run the wires to the junction box, so there is no ground wire coming from the panel, but the SJ wire has ground, so do I just connect it to the junction box?
6) Running metal conduit, how many 10 awg wires can I run in 1/2", 3/4" and 1" conduit?
I know this is a lot for a post and I thank anyone who took the time to read this, and even more for replies. :D
I need to install the following:
Table-Saw: 23.4 amp @ 220V 3 phase
Hinge Boring: 6 amps @ 220V 3 phase
Edge Bander: 16 amps @ 220V 3 phase
Line Borer (Future): 16 amps @ 220V 3 phase
Air Compressor: 15 amps @ 220V 1 phase
2 Dust Collectors: 6 amps @ 220V 1 phase X 2 = 12 amps @ 220V
I am figuring that the amps are in the place can do, since the machines will not all be on at the same time, and the existing breaker panels are mostly lights and office outlets.
Questions:
1) What is the difference between a load center and a breaker panel and where would you use each?
2) Can I eliminate the breaker panel to the left of the fuse box and add another 1 awg wire to the high leg lug nut, by replacing it with a bigger breaker panel? Each machinery will be on a dedicated circuit?
3) Can I use a 200 amps breaker panel instead of 100 amps so that if in the future I need to upgrade service, I won't have to do any rewiring?
4) I want to use 10 awg wire (12 awg will do, except for the table saw) and 20 amp breakers for all machines (30 amps breaker for table saw), is this safe?
5) I want to wire the machines with a quick disconnect plug, using SJ wire. Where do I connect the SJ wire ground? Do I connect in to the machine, the junction box, and how is the plug wiring connected? The SJ is running from the junction box to the machine with a quick connect. I am using metal conduit to run the wires to the junction box, so there is no ground wire coming from the panel, but the SJ wire has ground, so do I just connect it to the junction box?
6) Running metal conduit, how many 10 awg wires can I run in 1/2", 3/4" and 1" conduit?
I know this is a lot for a post and I thank anyone who took the time to read this, and even more for replies. :D