I want to put in a electric range with double ovens what wire do i use 8-3 or 6-3? thanks

Wgoodrich
February 15th, 2003, 07:39 AM
If all in one free standing range you must install a red black white bare or green conductor to serve as the range branch circuit. YOu may install 8 awg copper or 6 awg aluminum as a minimum size. Advise 6 awg copper or 4 awg aluminum as better option but not required. 50 or 60 amp breaker max on 6 copper or 4 aluminum and 40 amp breaker max on 8 awg copper or 6 awg aluminum.

You must have a four wire cable with a four prong plug and four wire range cord.

If these ovens are separate from the range let us know rules would be different.

Hope this helps

Wg

sting54
February 15th, 2003, 01:48 PM
I am switching from a gas oven/range to an electric double oven/range. It is all one. I have been told that I have to use 6/3 wire but have also been told that I can use 8/3 wire.

Wgoodrich
February 15th, 2003, 02:57 PM
As long as it is black, red, white, bare or green with a four prong range receptacly either 8 awg on 40 amp or 6 awg on 50 or 60 amp breaker is fine per 210.19 and 220.19 of the NEC.