View Full Version : Hot/Ground Reversed
mcarrio
July 13th, 2005, 05:04 AM
This is existing wiring and has not been modified in years. Monday several outlets on the circuit stopped working, while others still worked fine.
It did not trip the breaker. I used a tester. Working outlets showed correct. Failed outlets show hot/ground reversed. Tuesday, I went to troubleshoot the problem and all outlets were working and tested correct. I did the following: Since the wiring strings from outlet to outlet, I went to the last working outlet, (on Monday), and inspected the connections. The wires were pushed in the back of the outlet and not screwed onto the outlet, and the neutral wire going to the next outlets in line was barely in the hole. I attached all wires to the screws. I also checked all other outlets and removed wires from rear holes and also attached them to the screws. I checked a junction box which feeds some outlets and retightened the wire nuts and taped. I used the tester again and all test fine. I used a meter, and tested ground, neutral to hot = 120 V, hot to ground = 120 V, neutral to ground 0 V. I also replaced the breaker.
Questions:
In your opinion does it appear to have been a loose neutral wire ?
Is there anything else I can / should check ?
thx, Mark
Roger
July 13th, 2005, 08:14 AM
Yes you had a bad neutral connection or open due to those backstabbed outlets. These are notorious for this problem. You did the right thing moving the wires to the screws. When you use those outlet testers and the lights tell you that you have a hot/ground reverse this really is a open neutral indication. When you think about it getting the ground and hot connections reversed would be pretty darn hard to do, especially when you had a working circuit and then it stops working and you havent touched a thing. There are some people that think there are little green creatures running around in your wiring messing with you.:D The reason you get this hot/ground reverse as I understand is that with other loads plugged in to the circuit...lights, battery chargers etc when your neutral opens somewhere in the circuit you can actully read 120 volts from neutral to ground from backfeed through these other loads on the circuit. Your tester sees that voltage and indicates you have a hot/ground reverse. If you unplug all the loads on the circuit and unscrew the light bulbs and prevent this backfeed then the tester will change to an open neutral indication. Does this make sense to you?
mcarrio
July 13th, 2005, 08:31 AM
Thanks very much for your input. I understand what you are saying. I figured I was on the right track, but I wanted to here it from someone who knows about these things. This site was suggested from a co-worker. Great site !
thx, again, Mark
SuperNinja
February 16th, 2008, 02:40 AM
Thanks for the info, mcarrio and Roger.
I had the same problem today.
I messed around with trying to find the correct circuit breaker, and metering individual breakers, and pretty much wasting time.
So I did a search on the internet and found this thread, and using the info you posted, I was able to quickly find the source of the problem. (One outlet that had bad connections, wires plugged into the back of the outlet)
I moved the wires over to the screws, and everything worked fine after that.
Edit:
Looks like I spoke too soon.
The problem came back today, after a hair dryer was used on the circuit. :x
The hair dryer works ok on other circuits though.
Shontzy
August 23rd, 2009, 07:42 AM
The reason you get this hot/ground reverse as I understand is that with other loads plugged in to the circuit...lights, battery chargers etc when your neutral opens somewhere in the circuit you can actully read 120 volts from neutral to ground from backfeed through these other loads on the circuit. Your tester sees that voltage and indicates you have a hot/ground reverse. If you unplug all the loads on the circuit and unscrew the light bulbs and prevent this backfeed then the tester will change to an open neutral indication. Does this make sense to you?
Thanks a lot for this explanation. I was working on a sudden problem at my house for a LONG time and could not understand how the hot and ground could have gotten reversed. This really just means there is an open Neutral (white wire) somewhere on the circuit. When you have another area of the circuit with a load, that's when it would read hot/ground reverse. I had a light switch on the circuit, and when the light was "on" (the lights weren't working but there was power) the tester read "hot/ground reverse". When the light was off, it just read open neutral which was the correct reading.
To fix this problem, find the first outlet on the circuit that DOES work and make sure the neutral wire is properly connected. (The problem will either be with the first one that does work, or the first one that doesn't work which you have probably already checked at this point.) For me, this outlet worked but the neutral wire going to the rest of the circuit was loose so none of the other wires on the circuit worked. Once I tightened the wire, everything came back on.
flyrobert
October 31st, 2009, 02:30 PM
:party:great Info the same thing happend to me, I took of every outlet cover {5} and ceiling fixture even my outside lights all tested and all showed up as hot/ground reversed, came across this site, and wa-la I went to the only outlet that worked on the same circut. i would have never looked at that outlet, my next step was an electrician, on a saturday holloween day, $125.00 just to come out ouch... . ., and sure enought the ground wire was look it just fell out when i took the recepticle out and screwed it to the switch
and working lights
Thanks so much........