this question gave a 1 sentence scenario about a 300VA transformer bank consisting of 3 100VA transformers. Each transformer was 480V in and 120/208 out. The question was 3 parts:
1. find the amperage of the primary side if running 100%
2. find the amperage of the secondary if running 100%
3. if 1 XFMR is removed, what will be the new VA of the system?
1 & 2 I got correct, just by using:
300VA= 480v * A* 1.73 and..
300VA = 208V *A* 1.73
3 I got wrong. I figured 300-100=200VA. The correct answer involved something with 1.73. Where does the squareroot of 3 come into play for the third question? I knew to put it in the first 2, but can't see why it is needed for the 3rd?