Does anyone know how many branch circuits I need for a connected lighting load of 140KVA that consists of 120V fluorescent fixtures on a 20A circuits? I have a 120/208V 3 Phase Supply. Thank You! George
suemarkp
November 24th, 2006, 06:47 PM
I believe you'll need 73 if you're willing to max them out and the amps can come to exactly 16 (16A on a 20A circuit is for continuous use commercial). I'd plan for more than that. This is a tremendous amount of lighting!
pressone
November 24th, 2006, 07:29 PM
Hi Suemarkp,
Can you tell me how you came up with 73 branch circuits at 16A each by using the NEC guidelines for saftey?
Thank You So Much! George
mdshunk
November 24th, 2006, 09:08 PM
140 KVA is 140,000 watts
volts x amps = watts
watts / volts = amps
140,000 watts / 120 volts = 1,166 amps
code permits continuous loading of a 20 amp circuit to 80%
20 amps x .80 = 16 amp
1,166 amps total load / 16 amps permitted per circuit = 73 circuits
Is this for fluorescent aisle lighting or fluorescent high bays in a grocery store or a warehouse type situation? That's enough lighting to do 60,000 - 80,000 square feet. This is the sort of stuff that's generally done under an engineer's supervision.